Changing tails and paperwork

Former Community Member
Former Community Member
I have changed some tails and was wondering if a MWC would suffice .the work was carried out after a EICR carried out by another electrician who will remain anonymous ?. Cannot understand how 16mm tails fed from a 100amp cutout can be deemed as C1, there's no signs of overheating etc and the installation is around 30 years old, I personally would have given it a C2.
  • A C2 would still be unsatisfactory though, so wouldn't hugely change things. What is the actual connected load as opposed to fuse rating?
  • Well you're not creating a new circuit, so yes, a Minor Works Certificate would seem appropriate.

      - Andy.
  • Former Community Member
    0 Former Community Member
    Thanks Jewsbury that was my line of thought too.
  • Former Community Member
    0 Former Community Member
    Walsh,

    C1 immediate danger

    C2 no immediate danger but could become dangerous under certain circumstances


    Clear difference in my mind pal ??
  • 100A cut-out does not mean there is 100A fuse.
  • I agree that a MWC is appropriate.

    I think that the need to Code the size of the tails is marginal for a typical arrangement where the tails could be considered in free air.

    Unfortunately, Cable Rating Table 4D1A doesn't list installation in Free Air (Method F) for 16sqmm. However, if you take the ratio between columns 8 and 6 for the 25sqmm cable and apply this to the Column 6 cable rating for the 16sqmm then the 16sqmm has a rating of 100A (to 3 significant figures),


    Many of us will have seen or put in new 25sqmm Consumer tails and the Metering Co or DNO leave the old red and black 16sqmm Meter tails in position for a 100A supply..


  • Timeserved:

    Walsh,

    C1 immediate danger

    C2 no immediate danger but could become dangerous under certain circumstances


    Clear difference in my mind pal ??




    I wasn't suggesting that there's no difference, but pointing out that either way would be unsatisfactory and require remedial work. But whether there is an issue at all is less clear, not knowing what the actual loads connected are. 

  • Former Community Member
    0 Former Community Member
    Glad that's cleared up then ?