Fandango:
Question 2 - EVC's
We are looking at wiring 6 EVC points rated at either 11kw -22kw. They shall be fed from a public building in new underground ductworks. The building has it's own dedicated sub station believed to be a TNS. Because the Regs and COP make no ref to TNS I assume the EVC Charging points will not need any independant earth spikes ? Just to clarify that each EVC point cct will be protected at a dedicated Db located inside the building each fed by independant Type A rcds. The EVC Parking spaces will be located in the buildings shared car park adjacent the building 40m away. There is some existing column lighting in the car park which is fed from the opposite building which has it's own transformer. If we locate the EVCs more than 2.5m from any existing column lighting and street furniture fed off the opposite buildings supply then surely this will suffice ? Hoping its not a showstopper ?
411.3.1.1 Protective earthing
Exposed-conductive-parts shall be connected to a protective conductor under the specific conditions for each type of system earthing as specified in Regulations 411.4 to 411.6.
Simultaneously accessible exposed-conductive-parts shall be connected to the same earthing system individually, in groups or collectively.
Conductors for protective earthing shall comply with Chapter 54.
A circuit protective conductor shall be run to and terminated at each point in wiring and at each accessory except a lampholder having no exposed-conductive-parts and suspended from such a point.