John Peckham:
Andy
Thanks for the cue? Sockets with an integral RCD to BS7288 are not regognised in BS 7671, in fact they are excluded as BS 7671 only permis 3 devices for Additional Protection for use by ordinary persons.
SRCD sockets and FCU to BS 7288 can only be used where they have upstream RCD protection. I know that sparkles may think that is daft, wish it were not true or may disagree with me. If so I would commend they read BS 7288: 2016.
i would suggest Dave you fit an RCBO in the board, if it will not take one then fit an external RCD in an enclosure next to the board.
Posted by Alcomax on Nov 29, 2019 8:46 pm
John Peckham:
Andy
Thanks for the cue? Sockets with an integral RCD to BS7288 are not regognised in BS 7671, in fact they are excluded as BS 7671 only permis 3 devices for Additional Protection for use by ordinary persons.
SRCD sockets and FCU to BS 7288 can only be used where they have upstream RCD protection. I know that sparkles may think that is daft, wish it were not true or may disagree with me. If so I would commend they read BS 7288: 2016.
i would suggest Dave you fit an RCBO in the board, if it will not take one then fit an external RCD in an enclosure next to the board.Us sparkles do read BS7671. I have no particular inclination to read BS7288. BS7671 does have mistakes and the omission of SRCDs is one of them this time round. As far as I am aware JPEL/64 have acknowledged the error and this will be addressed in a future amendment, probably March 2022. So carry on fitting them. If you feel uncomfortable about the BS7671 typo, then you can always record it as a departure. Though, IMO, that is a bit pedantic for domestic works, but perhaps for non-dom, where there is an explicit contract to comply with BS7671:2018, it is maybe a good idea to record as a departure. You will still likely get a raised eyebrow from the more technically minded clients when trying to explain the reason for stating a departure.
John Peckham:
Alcomax
The omission of SRCDs I do not think a mistake by JPEL it is a deliberate decision otherwise it would have been included in the recent corigendum.
You say you would fit these as a departure from BS 7671. A departure is a deliberate act and must be no less safe than the provisions of BS 7671.Have a look at the extract below from BS 7288:2016 and after careful reading tell me if you think they are suitable as a stand alone device for Additional Protection?
This British Standard applies to residual current-operated devices (RCD)
incorporated in, or specifically intended for use with, single pole and neutral
and single pole and switched neutral and double pole socket-outlets, with
provision of earthing of the socket-outlet for household and similar uses (SRCD:
socket-outlet residual current devices). SRCDs, according to this standard, are
intended to be used in single phase systems such as phase to neutral. SRCDs are
only intended to provide supplementary protection downstream of the SRCD.
SRCDs are intended for use in circuits where the fault protection and additional
protection are already assured upstream of the SRCD.