John Peckham:
OK. I was trying to be helpful having some knowledge of the issue. Clearly my advice is un-welcome.
“Typically, the common form of protection for circuits supplying underfloor, wall and ceiling heating systems will be ADS. An RCD having characteristics complying with Regulation 415.1.1 shall be used for fault protection (I∆n ≤ 30 mA) (Regulation 753.411.3.2). This also meets the requirements of Regulation 753.415.1, the need for additional protection. It is a fundamental requirement of circuit design that overcurrent protection is provided, (Section 430 refers).
Typically, in older installations fuses to BS 3036 or circuit breakers to BS 3871 maybe found. Where this is the case and it is not practical to include RCD protection at the consumer unit a 13 A RCD spur maybe installed locally from an existing circuit as shown in Fig 2. Furthermore, consideration should be given to the power rating of the heating system and the implications affecting the existing circuit (Regulation 433.1.204).”
Please feel free to write a critique of the article.