Pat Eardley:
So why should I not rely on an SRCD?
I agree with your sentiment completely Chris but if the standard says I shouldn't do it then I cannot go against their express instruction. Here is a recent publication you may have already read that is a gamut of information on all RCDs but curiously when it comes to list all the BS numbers at the end BS7288 isn't there.
http://www.beama.org.uk/resourceLibrary/the-rcd-handbook---guide-to-the-selection-and-application-of-residual-current-devices.html
Thanks for replying GK, but if The product BS was not listed 10 years ago in BS7671, I am not entirely sure how it is more relevant that is still not included in the latest edition!
ebee:
"Aren’t the SRCD trip times faster?
Andy B. I`m not sure that this is the case.
Our old BS for RCDs was within 200ms at x1 wheras the EN we now all use is within 300ms at x1, which in itself makes our old standard appear superior.
However I find that in practice all of the functioning RCDs I`ve tested trip well within those times of both standards. In fact if I found one that approached say 90ms area I would be very alarmed as I once was when a pal of mine tested two RCDs on a connected circuit. We soon established the number of fridges/freezers running to be skewing the results.
Anyone else concour or disagree (mine is only a limited sample)?