Who here has first-hand of Tesla Powerwall? On cursory inspection, on-line technical info is sparse.
One of my regular domestic customers has had a quote for a Tesla Powerwall, including the Tesla isolating gateway to allow some property consumption in selected backup circuit(s) during network outage. Meanwhile I am quoting for CU upgrade to go in ahead of that work so that it can take place. The latter is basic work, no problems, were it not for the former which is providing me with a bit of a conceptual challenge. Now the first bit below is second-hand from the Tesla installer via my customer. Hence parts of it might be lost in translation, but as far as I have received from Tesla installer:
"Go ahead and to the CU, - it won't affect the Tesla."
The Tesla gateway contains SPD so I "don't need" to fit SPD in my CU. (But Tesla only up to 1KV, so not fully meeting AFAICT, 442.2.2)
Now the biggie: Tesla say they will be fitting a separate earth rod such that (as far as I understand it..), when the gateway entirely disconnects the network including earthing conductor (which after the supply head is no longer PEN 461.2).. then the gateway "islands" the whole property on the TT via it's switch 537.1.5. 551.6 .
Would it be "TT"? I would think that the system will go TN-S in island mode? At least that's what the IET Code of practice for electrical energy storage systems recommends. The earth electrode is required to comply with Regulation 551.4.3.2.1, and not necessarily to form a "TT".
Island mode (see BS HD 60364-8-82) is NOT associated with "TT island" as often used by the EV charging community ... which is why I really disagree with the use of the term "TT island" which does NOT appear in any of the standards, or indeed the IET guidance.
I'm not so familiar with switched alternative to public supplies, and in the absence of anything from Tesla, those who are able to might add to my reasoning below (or otherwise abuse it):
1) The property bonding and MET would still be connected to incoming PEN via gas/water pipe and next-door house(s).
This is the reason the system will go TN-S when in island mode. It's also the reason you can't easily generate a TT system in island mode.
2) What happens to the Tesla earth rod in normal (grid connected) operation? I'm guessing it's wired by the installer such it's effectively just a bonded extraneous conductive part.
It is nothing other than an extraneous-conductive-part in connected mode, although if the resistance is low enough it may help keep touch voltages down, on exposed-conductive-parts, or extraneous-conductive-parts, that are accessible outdoors, particularly away from the main building(s), in the event of a failure of the PME neutral conductor.
3) Under loss of network power, Tesla gateway disconnects incoming supply and TNCS earthing conductor and now floats on the parallel impedance of it's Ra and the bonding. During this time,the disconnected property would (due to high-ish Ra) likely get bootstrapped close to whatever voltage is on the incoming gas/water/bonding.
Is this the case? The recommendation of the IET CoP are to leave the distributor's means of earthing connected, but to isolate the Live Conductors of the supply.
4) Although there are two earthing systems, there aren't two simultaneously accessible earthing systems.. Because in normal (network) use the TT electrode would be just a bonded extraneous part, and in "island" mode the TNCS earthing is not connected, - But to make this claim, we'd then need to also state that the TNCS "not-MET" (with installation earth no longer connected) was a bonded extraneous conductive part.
To separate them would require a suitable distance below ground of all parts connected to the PME, and everything connected to the TT system. This is in practice in most domestic premises at least, not achievable, not least because of extraneous-conductive-parts, hence the recommendation to leave the distributors means of earthing connected, and to isolate the live conductors (each L, and N). N isolated to prevent two N-E bonds, which causes all sorts of havoc, although I fully appreciate that technically it remains connected via the means of earthing.
5) Loss of PEN externally: The Tesla I'm guessing would detect any possible lift in earth potential of the TNCS MET and could then switch into a safe condition (house disconnected entirely, other than bonding to PEN), and un-powered, or even maybe continue to generate for the house backup circuits, while floating on whatever fault condition PEN/bonding voltage was imposed on it.
Not sure of that ... unless it contains a means of detection according to 722.411.4.1 (iii) of either BS 7671:2018 or BS 7671:2018+A1:2020.
Have I reasoned this out right?
davezawadi:
I cannot see why anyone should buy one of these products, simply because we do have continuous electricity supplies and the life of lithium batteries so far has proved to be 500 - 1000 full cycles if you are lucky. That might be OK in a car (100,000 miles say), but it is probably only 3 years if you really want to make use of your solar electricity. It will be interesting to see how long these batteries last, and Tesla may well have a better product than those from elsewhere, but I would rather not take the risk from lots of experience with batteries for broadcasting etc.
justinneedham:
This is all worthwhile. Thank you..
Skipping over for the moment the practicalities of the system.
Graham writes "I would think that the system will go TN-S in island mode? At least that's what the IET Code of practice for electrical energy storage systems recommends. The earth electrode is required to comply with Regulation 551.4.3.2.1, and not necessarily to form a "TT".
- I will buy the COP, but before I receive that. You imply TN-S? This and all the adjacent properties being TNCS right now. Even if it were connected TN-S at the supply head, it would more-or-less be TNCS via the neighbours bonding to the gas.
Since consumers are not generally permitted to combine N & E functions in a single conductor in their installations according to ESQCR, the arrangement in island mode can only be described as TN-S.
However, as you correctly point out, the arrangement will remain connected to the PME earthing system (but this may well be the case anyway because of extraneous-conductive-parts). Therefore, certain provisions regarding the use of the PME earthing terminal continue to apply to the installation in island mode as well as connected mode.
Mike writes "having a system where you wish to load shed when on inverter really does affect the CU layout.., "
Indeed yes. I didn't want to complicate my original post on this, but that's something else on the list for my customer who wants this facility but doesn't necessarily understand the considerable potential for extra wiring complexity.
This is also discussed in the IET CoP.Ultimately the easiest approach may well be two CUs, one with "connected mode only" loads, and the other which is energized in both connected mode and island mode.
I will add a final twist.. The Customer has an early-adopter EV charger also. Installed when external use on TNCS still had the "reasonably practicable" get-out in 17th edition. The unit is fitted just inside up-over garage door, alongside the consumer units, and is exclusively used outdoors, cable under the swing-door. Customer has suggested pulling the EV charger into the new CU.. all very well, but I've turned this down since I can't fulfill the need for a fully isolated TT. Meanwhile I'm told that Mr Tesla has suggested "fixing" the problem by connecting it to "his" new rod, - This not quite worked out comment is where my original puzzle came from.
If Tesla is serous, then this is either:
A) Implying that the new rod is separate from the incoming earth in his installation, yet to use it and connect the EV charger would be ignoring inevitable proximity to the alternative supplier earthing system. Non starter then on two counts, because we've discounted the former (rod is connected to the PME) and the latter (proximity of two earthing systems).
..or B) The new rod will miraculously meet Annexe A733.3 for 70V touch voltage. - Not a chance in hell.
Agreed here - the earth electrode resistance will be tricky.
An alternative approach may be to use an open-PEN detection device. HOWEVER ... there are some tricky nuances here also:
I am going to conclude that Tesla might be a little unclear about things in that respect, - or this is Chinese whispers playing havoc.
Plan:
Don't do anything about the EV charger- leave it alone on it's existing CU, because I can't change it at all without replacement with a fangled one having monitoring device 722.411.4.1(iii).
You could argue it complied with an earlier version of BS 7671, and you've not made things worse.
Issue relevant text about the above.
Find out if customer really wants backup circuits and if so to spell that out to me ASAP.
Backup of all circuits isn't really practicable - probably not recommended by Tesla either?
Fit new CU (with or without second backup circuits CU), and let Tesla get on with their bit.
Agreed