AJJewsbury:
If it helps at all, here are some diagrams (originally done for the old Forum) for the usual layout for switched alternative local generation (the principle is the same whether it's a petrol generator, or battery and inverter, or anything else).
The first one shows the simplest case of everything TN-S - and how the generator is configured/earthed in just the same way as the DNO supply in a nice symmetric layout. When connected to the DNO's supply (and the generator off), the DNO's electrode provides the means of earthing and the local generator's earth electrode is nothing more than one more extraneous-conductive-part. When the DNO supply is off and the generator running, the local rod provides the means of earthing and the DNO's earthing system is just another extraneous-conductive-part as far as the installation is concerned.
Then what you're more likely to have in practice, with a PME supply and an RCD very soon after the generator (as most small generators/inverters won't be able to produce the large currents needed to open overcurrent devices for ADS) - so some of the symmetry is lost, but the underlying principle is the same:
- Andy.
Whilst these arrangements are absolutely OK for a switched alternative to the normal supply, and illustrate very well the situation about leaving the distributor's means of earthing connected, I feel it's only fair to readers to point out that they won't support either self-use or export of stored energy in connected mode. Therefore, switching for island mode in a prosumers' electrical installation is a little more tricky, involving switching of an N-E bond. This is because you can't have two N-E bonds at the same time ... and BS 7671 doesn't permit you to rely on the supplier's N-E bond even in PME.
though from a safety point of view it raises questions about avoiding failure modes that leave the system either un-earthed
Something I don't see in that Tesla diagram is how does the inverter know if it is meant to be in grid-tied mode or islanded mode? A grid-tied inverter should automatically switch off if it sees a mains failure. I would expect an extra signal, perhaps an additional contact on the big isolator switch.