Sparkingchip:
The other issue is that when I did the testing course and we were told that we only test 30 mA RCDs at x 5, because generally shoving half an amp through a domestic earthing system and electrode to test a 100 mA RCD is getting risky.
Andy B
500 mA should be more than enough to fire a 300mA RCD in < =200mS. If not, then there will be something else wrong. The "2 times" is arbitrary. The name of the game is that the RCD [ s type ] is quick enough.
Sparkymania:
Sparkingchip:
And testing Hager Type A 30 mA RCDs has not been mentioned. ?
What's the issue with these?
Sparkingchip:
The other issue is that when I did the testing course and we were told that we only test 30 mA RCDs at x 5, because generally shoving half an amp through a domestic earthing system and electrode to test a 100 mA RCD is getting risky.
Andy B
I don't see any issue with half an amp through a domestic earthing system.