Sparkingchip:
So can they leak more than 6 mA D.C. ?
Hence the preference for a dedicated EV charging circuit, even if it is only a 13-amp socket?
AJJewsbury:
Hence the preference for a dedicated EV charging circuit, even if it is only a 13-amp socket?
But BS 7671's idea of a circuit considers only overcurrent protective devices, not RCDs - so you could have a separate circuit for the EV point but still have the upstream RCD shared with other circuits (e.g. as in split load CUs).
Operating Voltage |
---|
230V AC 50Hz |
Max Current |
---|
13A |
Rated Trip Current |
---|
30mA |
Trip Speed |
---|
Less than 40ms at 150mA residual current |
RCD Type |
---|
Double pole – Passive (Latching) |
Breaking Capacity |
---|
250A (Earth leakage) |
Continues to protect with |
---|
Lost neutral/pulsating DC earth fault |
Operating Temperature Range |
---|
-5°C to 40°C |
Chris Pearson:
AJJewsbury:
Hence the preference for a dedicated EV charging circuit, even if it is only a 13-amp socket?
But BS 7671's idea of a circuit considers only overcurrent protective devices, not RCDs - so you could have a separate circuit for the EV point but still have the upstream RCD shared with other circuits (e.g. as in split load CUs).Yes but ...
722.531.2.101 "... each charging point shall be protected by its own RCD ..."
If the circuit is in say a garage, it might be clipped direct, in trunking, or in conduit, so no need for the RCD to be in the CU. If the EVCP is on the side of a house and the cable is buried in plaster, it will need an upstream RCD. If that is not an RCBO, there will have to be another one locally.
Sparkingchip:
LOL.
These tick a lot of boxes!
Operating Voltage
230V AC 50Hz
Max Current
13A
Rated Trip Current
30mA
Trip Speed
Less than 40ms at 150mA residual current
RCD Type
Double pole – Passive (Latching)
Breaking Capacity
250A (Earth leakage)
Continues to protect with
Lost neutral/pulsating DC earth fault
Operating Temperature Range
-5°C to 40°C
If you consider that we have plug-in petrol hybrids, which also have to meet the standard, then, just like with aircraft (even though aviation kerosene is normally only explosive in vapour form) avoidance of static is seen as important, through earthing the fixed electrical ground power, and also providing static discharge for a tending bowser. Earthing is even required for the topologies of Mode 4 rapid chargers that include electrical separation (see Annex K of the 4th Ed of the IET CoP for EV Charging Equipment Installation).
In addition, there is a requirement to install EV charging in the curtilage of petrol filling stations. Avoidance of static is important there too.