davezawadi (David Stone):
Well Graham, perhaps you have hit the nail on the head. I like to do testing with 2 people with radio communications, it is very much quicker, and overcomes your idea that an open accessory or whatever left with a meter and perhaps a warning notice is dangerous to anyone. The idea that one man tests a large installation by walking miles each day is simply arcane.
We are in the 21st-century and need to use 21st-century tools. R1 + R2 testing takes very little time, insulation testing has someone close to the items being tested etc. You can see how this is so much safer and quicker but want to give a method statement and procedure which removes the value of the work.
So be it, but I hope there is never a problem due to inadequate testing, it is likely one day. Personally I have no problem with live testing at all, but then I am of that age.
Sparkingchip:
With many light fittings now being LED without a removable lamp you cannot even fall back on some of the aids to safe working.
So for the EICR you need to confirm the polarity at the fitting, single pole switches and breakers are in the live phase, loop impedance and possibly the RCD trip time.
Is opening the ceiling rose of a pendant, which does not require any tools to test anymore dangerous than removing the cover of the consumer unit to test Ze, etc?
Andy B
Sparkingchip:
. . . There is a precedent.
https://www.manchestereveningnews.co.uk/news/greater-manchester-news/dads-agony-after-apprentice-electrician-9085985 . . .
There may be a precedent, but as far as I can see, that is not it. The electrocution occurred whilst getting to the point of work, due to the travelling crane not being isolated, not as a result of tests being carried out at the point of work. I am of course assuming that this was an approved method of getting to the place of work.
Alan.
Sparkingchip:Is opening the ceiling rose of a pendant, which does not require any tools to test anymore dangerous than removing the cover of the consumer unit to test Ze, etc?
Andy B
Polarity Test can be a dead test, and in that respect is far less dangerous than removing the cover of the consumer unit to conduct live tests.