Sparkingchip:
I cannot think of any installation dead tests that cross wired installation would not pass.
Andy B
Indeed Andy. It looks like the tester you are using is of the type that would alert you to a live line conductor even if another potential was not available. Some testers do not offer that facility and one needs to be careful as say a polarity reversal on a TNCS system would not be apparent when tested at a single-phase intake.
lyledunn:Sparkingchip:
I cannot think of any installation dead tests that cross wired installation would not pass.
Andy BIndeed Andy. It looks like the tester you are using is of the type that would alert you to a live line conductor even if another potential was not available. Some testers do not offer that facility and one needs to be careful as say a polarity reversal on a TNCS system would not be apparent when tested at a single-phase intake.
It self tests as well.
Andy B.
gkenyon:Sparkingchip:
I cannot think of any installation dead tests that cross wired installation would not pass.
Andy BSo a Ze or ZDB test could check for a supply wiring error? I think that's back to where we were - discussing live Zs tests on ALL final circuits.
You have to do a live test somewhere along the line.
Three phase you will be checking the phase sequence as well as polarity, I had an interesting discussion with two electricians in a pub one night, one of them works for a generator hire company and makes great use of a long wander lead to ensure he is hooking up temporary supplies correctly.
Andy B.
Sparkingchip:
In the back of my van I have a telescopic fibreglass R2 testing pole, I used it to test a light on the gable of a house a couple of weeks ago, I don't intend to take an extension ladder to check a light such as that for an EICR, visual and continuity testing with both feet on the ground.
However when replacing a light fitting and access equipment is already in place then I would loop test, as these were site cabins being installed that were already being wired before delivery to site some testing is required, if need be I would test at a switch with two feet safely on the floor, but obviously that may require a two lead loop tester and I have a couple to use.
There is a precedent.
https://www.manchestereveningnews.co.uk/news/greater-manchester-news/dads-agony-after-apprentice-electrician-9085985
Andy B.
We can keep going around in circles with this, the simple truth is we need to choose the time and the place to do live testing, personally I avoid doing it on top of a ladder or the like, but you may still need to prove dead.
I remember going to look at a faulty outside light one wet winter evening, I climbed up the aluminium ladder thinking it may just need a new lamp in it and without touching the light fitting put I one probe of the voltage detector on the ladder and the other on the light fitting, it lit up like a Christmas tree so I climbed back down the ladder and started to put it back on the van, the lady customer enquired what I was doing, my reply was going home then coming back when it is light and dry as I wasn't going to mess about with it in the wet and the dark.
Sparkingchip:You have to do a live test somewhere along the line.
Three phase you will be checking the phase sequence as well as polarity, I had an interesting discussion with two electricians in a pub one night, one of them works for a generator hire company and makes great use of a long wander lead to ensure he is hooking up temporary supplies correctly.
Andy B.
Agreed - but perhaps we need to consider whether it's a loop impedance test when we have lots of microgeneration sources out there. The results using current test methods could well be largely meaningless.