Legh Richardson:
The manufacterers state you can't mix different companies components together in the same enclosure although You might not be able to avoid this when using SPDs and AFDDs with MCBs etc
Well, BS 7671 says you can use components from different manufacturers, BUT you become responsible for the if the use of a particular component deviates from the original assembly manufacturer's instructions (Note 2 to Regulation 536.4.203).
Whilst there is no legal precedent that I'm aware of, the legislation for the relevant Directives does really lead you to that conclusion.
In this particular case, a DIN rail is only a mounting standard, not a standard that invites you to make whatever modifications you like to the assembly that includes it.
Where does this leave the empty "adaptable enclosure" with a DIN rail? Well, when you assemble a variety of products from different manufacturers into that kind of empty enclosure (and I'm not talking about a consumer unit here, where you're assembling in accordance with manufacturer's instructions), you become the assembly manufacturer. The assembly itself is not covered by BS 7671, see Regulation 113.1 (second sentence). So, if you're buying DIN rail products, if you want to avoid being an "assembly manufacturer", use the enclosure from the relevant range of products from the DIN rail product manufacturer, in accordance with the manufacturer's instructions.
mapj1:
If the folk doing the mix and match are happy to be the 'manufacturer' and have designed it with sensible current ratings and so forth, then they are fine. They have no comeback on the component makers if their sums are wrong and it all melts however.
What hazards and failure modes have they overlooked?
Do,nt know,but they were suggesting I copy their design,which I,m not prepared to do.
Regards,Hz
Sparkingchip:
Are you going beyond the requirements of a fixed installation EICR and moving into machine and appliance regulations?
Andy Betteridge
This is a great question, because when you talk to some people in the industry about the extent of an EICR (or even initial verification), they believe that you will, say, do an earth continuity test to an appliance connected to a fixed connection unit - yet the appliance, and where applicable its pre-fitted connecting cable, are outside the scope of BS 7671.
Regardless of the technicalities in standards regarding the rights and wrongs of this belief, in my experience those carrying out initial verification and EICRs go up to the point of connection of an appliance or machinery, and no further - the usual exception being lighting where the fixed wiring is brought into the luminaire.
Why is this a good thing to have a discussion about?
Well, the person ordering an EICR might be under the impression that they've had the earthing of their fixed appliances checked ... when in fact it's been omitted, often with very good reason ... for example with appliances having a mix of means of protection against electric shock:
So, as an example, what happens when the landlord has his regular check, but there's a problem with the protective earthing in an electric wall-mounted radiator or towel-rail, and someone gets a shock?
Sparkingchip:
I did an EICR yesterday for a house purchaser, the vendor was at home and enquired what the long green wire is for, as in my wander lead. I explained that in a house like his with metal faced fittings and lots of metal light fittings it is the quickest and easiest way of ensuring things that need to be earthed are.
The range cooker was checked by dabbing the probe onto the screw of the wall mounted switch and the appliance itself, the shower had to have its cover removed.