The lighting circuit has no CPC (earth), this is not uncommon in older houses. For that reason all light fittings are Class 2 i.e. plastic with no metal, and there is a clause in the tenancy agreement which forbids tampering with the light fittings (this is a house we own and rent out).


Previous EICRs did not even mention the lighting circuit because of the Class 2 fittings. I have just got a new EICR with an observation "lighting circuits have little or no earth" and classification code C1 ("Danger present, risk of injury, immediate remedial action required"). The overall assessment says "Unsatisfactory" with the comment "Needs updating to current regs". This can only be fixed by a complete rewire of the whole lighting circuit.


This is pointless, there are no earth connections in the plastic fittings.


Any thoughts? Many thanks.
  • Only if there’s wall lights.


    Most houses have the light switches either side of the central hall wall on the ground floor, generally you can get a run of boards up along the landing and into bedrooms then work from there the using rods from the centre light positions.


    And surprising you can often pull cables down the wall behind the capping.
  • Sparkingchip:

    And surprising you can often pull cables down the wall behind the capping.


    I assume that you pull in the new cable as you take out the old - how do you join them?


  • Chris Pearson:
    Sparkingchip:

    And surprising you can often pull cables down the wall behind the capping.


    I assume that you pull in the new cable as you take out the old - how do you join them?




    I'd cut away about half the width of each cable for 6" or so at the end of the new and old cables - place the cut edges together to and wrap tightly with insulating type (just overlapping) starting from the end that'll be drawn in last - that way you have a reasonably secure joint that's only a fraction of a mm thinker than the cables and should draw through most holes that the original cable fitted through.


      -  Andy.


  • I've done this a few times, success rate about 90% if it moves at all, not worth trying if it does not - you need to form a very flat joint, in the manner of a running splice, so the 3 (or 2 in this case) cores have their looped sections not side by side.

    Do not bother if you and accomplice cannot get the wire to move up and down an inch or 2 behind the capping with sensible hand tension. before even doing this give both ends a quick go with the hoover - a sharp edged  'snot' of  plaster dropping in at the wrong moment could jam it solid.


    Assuming so far, you are in  with a chance...

    Working from above, so gravity is on your side..

    So remove the outer jacket for 4-6 inches on both the old and the new. Strip L and N offset so that there is one with about 1.5 inches of bare copper, and one with more like 3.

    form loops with the round nosed pliers, and then wrap back, or do the western union splice of (page 7 this PDF) set both splices offset, and rebuild with tape to re-create jacket profile, or at least something with no great lumps or steps in diameter. A quick massage with either washing up liquid or that fancy stuff plumbers use (no tittering at the back) to make the cable slippy. Accomplice feeds in as straight as poss with no kinks or twists, while you pull from below.


    If there are 2 cables behind common trunking they will have to be pulled as a pair.


  • Andy, Mike, interesting methods. Of course, what you really don't want is the ends coming apart.


    I have had some success with stripping back a short length and then soldering the ends together. Then a small wrap so that the aft sheath does not catch. I reckon pull up 'cos that won't bring any builder's carp with it.


    Whatever you do, make sure that you pull on the correct cable. ?
  • And use 1.0 mm twin and earth, not 1.5 mm again it’s surprising how much difference that makes pulling cables to replace old cables.
  • cc6232fa636e55a2fc1dcb4de6d10c6a-original-20200922_185653.jpg
  • Look at a typical semi that hasn’t had the lighting circuit altered in fifty years or more, there aren’t light switches on the perimeter, they are generally all down the middle and accessible from above by lifting boards on the landing and third bedroom, though the kitchen being under the bathroom can be a bit of a sod.
  • But just hope that some tight wad electrician did use all the odd bits of capping up leaving a sharp end on the join part way up the wall. Indeed you may need to bend the ends of the capping back if it wasn’t done in the first place.
  • Former Community Member
    0 Former Community Member
    Or that the brick/block layer left the mortar joint "squished out" rather than trowel it off!


    Regards