Sparkingchip:
You need to get an opinion from an electrician who can actually have a look at the installation, I don’t know what to suggest regards finding an electrician to do do. [sic]
Well I think that the owner is stuck between a rock and a hard place. There seems to be a sub-optimal EICR, but if she gets another one, why should it be any better and you still don't get around the no RCD no CPC lighting circuits.
On the other hand, the purpose of the new legislation is to safeguard tenants from these shoddy installations.
Being pragmatic, is the inspecting electrician prepared to remedy the issues highlighted above or can you get another electrician who would remedy what needs to be done (CU change?) and issue a satisfactory EICR?
AJJewsbury:Max permitted Zs column isn't right. Max Zs for a 30 A BS 3036 fuse is 1.04 Ω (Table 41.2).
That's 'cos they've decided that 5s disconnection times are appropriate for all the final circuits ?
It's complete nonsense (he said politely).
- Andy.
The entry for the maximum Zs is generated automatically after you enter the disconnection time, type and rating of the fuse or circuit breaker.
As I said above if you correctly complete the schedule of inspections the observations are entered ready for you to edit with references.
Use the software properly and you end up with a report in which everything tallies up and makes sense, unlike this one.
Andy B.
Mutley:
it needs a total rewire for few grand.
What I want to know is can I ask info on here about the codes he has put and if reasonable.
Mutley:
The lighting circuit would be easy to re wire as the back boxes are all connected with iron/galvanised barrel or something. So straight forward to pop new cable down.
The owner is keen to get this fixed ASAP and is happy to pay what ever it takes as the Agency are telling her she risks a 30k fine to get it done ASAP.
That's great. The £30k is a penalty and not a fine and I think it is regrettable if the landlady feels threatened by it.
It isn't necessarily "straight forward" to pull cables up and down conduit or capping - it can be a doddle or it can be a ***. Good luck!
John Peckham:
Looks like the usual nonsense from a person not competent to carry out a periodic inspection and test.
Nice phrase JP.
Having said that I have myself been known to make comments ref remedials if they are defects noted by someone else not me. When there`s a few it can get to the point where you get to consider if " a total rewire might be the most prudent course of action" of course a site visit sometimes starts to make that answer a bit clearer.