Nikp:Sparkingchip:
Domestic smoke and heat alarms have mains voltage throughout their circuit.
Testing domestic smoke and heat alarms should be carried out following the manufacturers instructions, by pressing the test button.
The expiry date is on a label.
I don’t really do much on domestic side, but don’t they normally have a shelf life of ten years, and if peeps really wanted to test surely buy a can of smoke.
That's my point - it's more than the test button. I have a few Montecristos from my visits to Gibraltar. Would they do?
davezawadi (David Stone):
There you are Andy, you can do that, but it needs to be in the limitations box, "Only test buttons pressed". Real fire alarm system tests need smoke, heat, thermometers, etc to check full functionality.
You can also use bubble wrap for real fire alarms, works a treat when testing high beam detection.
The earth is so that the panel can flag a wire to earth fault if cabling insulation is mechanically damaged- a positive to earth fault or a negative to earth fault means the cable has been spiked, but the rest of the self test to see the terminator resistor may still pass.
As I see it the earth (C.P.C.) wire and "tin foil" are used with FP200 cable just because they are integral to the cable. The fire alarm panel will detect a fault if a nail is driven through a cable even if it is not earthed, in these cases.
1. Broken positive conductor.
2. Broken negative conductor.
3. Short between the two above.
Earth NOT needed in all three cases.
The cable only carries 24 Volts at a tiny current. And all components are made of plastic. Earth not needed.
Perhaps the screen protects the cables from strong magnetic fields or radio interference. I am not really sure on that.
Z.
wallywombat:
My (admittedly vague) understanding of the foil in FP200 cable is that it's not for any shielding or earthing purpose, but as a vapour barrier to stop hot and possibly corrosive gases (perhaps oxygen??) initially attacking the inner layers.
Yes, this stuff.
https://www.bing.com/videos/search?q=youtube+FP200+cable&docid=608017582824820065&mid=6D3E9BC3C569513031576D3E9BC3C56951303157&view=detail&FORM=VIRE
Z.
1. Broken positive conductor.
2. Broken negative conductor.
3. Short between the two above.
Earth NOT needed in all three cases.