davezawadi (David Stone):
The real problem is exactly where fixed wiring and appliance cross over. I think a normal fire panel system (24V normally) is an appliance. The wiring is part of that appliance and does not come under BS7671.
Make your mind up Dave!
https://communities.theiet.org/discussions/viewtopic/1037/27608#p155414
Weirdbeard:davezawadi (David Stone):
The real problem is exactly where fixed wiring and appliance cross over. I think a normal fire panel system (24V normally) is an appliance. The wiring is part of that appliance and does not come under BS7671.Make your mind up Dave!
https://communities.theiet.org/discussions/viewtopic/1037/27608#p155414
The output side of the alarm panel is still classed as fixed wiring and also as a safety circuit, it still needs to be installed as all other lv wiring systems in BS7671, needs to be supported correctly etc throughout it’s entirety. We may only record the 230v side on the EIC, however the system itself has another test certificate to record results such as IR and Impedance etc.
Sparkingchip:
Hardwired smoke and heat alarms are a fire alarm system and their installation is within the scope of BS7671, you cannot just ignore them when you are doing an EICR.
If you are not inspecting and testing the wiring for an alarm system of any type for an EICR you have to specifically state on the EICR that they are excluded from the report and the client needs to get a report from a specialist company.
How an electrician or inspector could justify not inspecting and testing a mains voltage smoke alarm circuit for an EICR is beyond me, as is how they could inspect and test the smoke alarm circuit but not say that the actual alarms are not fit for purpose, because for example they expired several years ago.
The heffalump trap here is whether you I&T the alarm system - i.e. does it function as it should? If you are going to do that, you will need appropriate training and PI insurance.
I suggest that it is sufficient to unclip (a sample of) the smoke/heat alarms and inspect the cable and terminations. Then do IR (if you have not done a whole board check), Zs, and RCD (if fitted and not already tested) on the circuit as with any other circuit.
As for a panel system, I would stop short at inspecting and testing the supply.
Sparkingchip:
Domestic smoke and heat alarms have mains voltage throughout their circuit.
Testing domestic smoke and heat alarms should be carried out following the manufacturers instructions, by pressing the test button.
The expiry date is on a label.
I don’t really do much on domestic side, but don’t they normally have a shelf life of ten years, and if peeps really wanted to test surely buy a can of smoke.