ebee:
Sorry Zoom I do not agree.
Where a genuine F1 applies it could be something that is a C1 or a C2 lurking there and as such we`d condem.
However it could be a C3 or even no code at all.
Until it is investigated and therefore determined we must make it condemable. We can`t give it a pass (yet) or a fail (yet) we can only record a potential unsatisfactory as a (assumed) unstisfactory. Therefore F1 unstaisfactory
An F.I. means that we have not completed our job. It is a cop out, get out of jail free card. If we can not gain access to a locked room we report so. We do not put F.I. and then condemn the installation. We can't report on don't knows. The report can't be completed until we do gain access to the locked room and its electrics.
The report is not complete until the work is finished. In this case the work of inspection and testing.
If the customer asks why an installation has "failed" he won't be happy because we say further investigation is required. He has a right to say: "Well get on with it then".
Dave Stone would not disconnect a cable where it could not be identified as to its use or destination. Andy is concerned about a live unidentified cable perhaps with loose live ends, hidden under the floor, or in the loft sitting there ready to bite somebody such as a plumber.
Z.
ebee:
Chaps,
I would hope you`d ask why they`d want an EICR before commencing.
Evidence of poor previous work or just contentment of knowing it is satisfactory. That would decide whether you might make free minor corrections without referring back to them
Absolutely. If I take out a fuse from a switched fused connection unit supplying a gas boiler system that should be a 3 Amp size, but find a 13 Amp fuse instead, I change it there and then. It is easier to put the correct size fuse back than do more paperwork. Then I do not have to worry about that again. I have also done that with fuse wire as well in older installations. Who wouldn't? Tight time constraints cause cut corners.
"Where an observation requires further investigation (FI) because the inspection has revealed an apparent deficiency which could not, owing to the extent or limitations of the inspection, be fully identified and further investigation MAY reveal a C1 or C2 item, this should be recorded within section K, given the code F1 and marked as unsatisfactory in Section E." P. 475 B.S. 7671.
If we are to assume guilty until proven innocent, then FI should be done away with and a C2 used in its place. FI causes confusion and is an unnecessary duplication.
Z.
AJJewsbury:It's all a matter of contract.
Absolutely.Rectifying minor faults as you go along is just good practice.
But only if that's been agreed with the customer. If they've asked you for an EICR because they suspect a previous electrician hadn't done a good job, they might not thank you for quietly sweeping problems under the carpet or 'destroying' the evidence.
And they certainly would not appreciate the flickering lights and intermittent appliance operation, or the house fire caused by the loose terminals which you left behind.
Z.
It's all a matter of contract.
Rectifying minor faults as you go along is just good practice.
keylevel:Zoomup:How can you say it's unsafe if the inspection and test has not been fully completed? Surely in this case an F.I. is the lazy way out.
You can't, but neither can you say it's safe - there are three possible states - "safe", "unsafe" and "unknown". Only "safe" allows the condition to be declared as "satisfactory".
So should we continue to inspect and test until we have found the end of the unknown cable or disconnected it? A two minute disconnection is preferable to a fail surely. Does a single F.I. equal a fail? I have even corrected a wrong connection at a consumer unit where two ring finals are crossed over at two 32 Amp M.C.B.s in error. It is no trouble to do that as the ends are already disconnected for testing anyway.
Edit. Add: I feel that we would be obliged to disconnect the unknown cable as not doing so would be negligent. To liven it up again could lead us into great trouble.
Z.