BS 7671 417.3 Placing Out Of Reach
I would like to ask what the distances 0.75m and 1.25m on the illustration drawing from the surface expected to be occupied by persons refer to, No explanations of the same is given in IEC 60364-2-21-1993 page 6
  • Amos Owaga:
    Well, Fig. 417 refers to arms limit of 1.25m
    417.3.3 refers to places where bulky or long conductive objects are normally handled etc. where clearance distances may have to be increased, taking into account the relevant dimensions of those objects.
    2010 34 Spring Wiring Matters (theiet.org)
  • The 0.75m is the distance you can reach under the floor you are lying on  - so like hanging over the side to reach something under a platform  or reaching under a plat form or through an access like a trap or hatch for example,  that you cannot pass your head and shoulders through.
    Note that this is an absolute minimum and assumes no credible use of hand held tools, cameras or what have you that increase the distance you might make contact. In nearly all real cases, the distances end up being  increased a bit.