davezawadi (David Stone):
I will now set the cat amongst the pigeons.
You are doing an EICR, is anyone going to code any of the suggestions above?
Let's see...
FI ... ?
I can't say I disagree that the current situation can make it very hard for those carrying out EICRs.
For example, I know there are installs of commercial laundry machines, where additional earthing (due to high protective conductor current) is required, and not provided. That's a potential breach of Electricity at Work Regulations (earthing not adequate) if there's a problem with the primary cpc. Yet, how would an electrical inspector know? Or the Duty Holder for that matter?
But, how is that any different to portable appliance testing that fails equipment just because the person employed to do the inspection and testing isn't aware of the design of a particular appliance - I've seen that lots too. Or the company who decided to change all the fuses in the BS 1363 plugs on monitors in the office I was working in from 13 A to 3 A based on power on the rating plate - within a week, most of the 3 A fuses had blown due to inrush !
However, the current situation is, that if a product comes without a pre-fitted "standard plug", you can't make assumptions about whether it's OK to use a particular protective device, as with this gas hob - if it came without a plug, and the manufacturer's instructions state a particular rating of protective device, that's what it is, which for UK market might be a 3 A fuse ... or it might easily also be a 1 A fuse in the FCU !
Not a good situation, but an issue for product standards ... and many of them say something similar in this regard.
davezawadi (David Stone):
I will now set the cat amongst the pigeons.
You are doing an EICR, is anyone going to code any of the suggestions above?
Let's see...
This sounds like a C&G exam. ?
At the beginning, I would ask the householder if there were any concerns. Next I would have a look and smell - I assume that I shall find nothing.
Then I would have a look behind the plate of the cooker switch - not possible to do a sample! On the above information, I wouldn't expect to find anything amiss. Then I'd have a look behind the plate of the FCU. IR testing might be limited if there is a neon. I'd check Zs at the FCU. And that's about it. I would not remove the cooking appliances.
So my only concern might be over-filled load terminals on the FCU. That's when it gets interesting! I wouldn't be entirely happy with say only two threads engaged, but if the cable passes the tug test, so be it. If the cable turned out to be loose then we have a problem. Do I attempt to put it back? I think that I would want to speak to the householder at this stage. If (a 4 mm²) cable cannot be secured, then I think C2. If it can be, then no code. (Which I think is the point that Dave was making.
Was I over-thinking the question? ?
gkenyon:. . .
But, how is that any different to portable appliance testing that fails equipment just because the person employed to do the inspection and testing isn't aware of the design of a particular appliance - I've seen that lots too. Or the company who decided to change all the fuses in the BS 1363 plugs on monitors in the office I was working in from 13 A to 3 A based on power on the rating plate - within a week, most of the 3 A fuses had blown due to inrush !
. . .
It is not compatible with fuse ratings on a consumer unit, where you will not find a rating less than 5 A.
I presume the reason for this is to "officially protect" the IEC C14 plug, which is rated at 10 A. However I would not be overly worried if a 13 A fuse were fitted. The fuse is to protect the lead and the connector at the other end, but not the monitor, which should have is own internal fusing.
gkenyon:
Table 2 of BS 1363-1, which is actually referred to in the Plugs and Sockets (Safety) Regulations, now lists 3 A, 5 A, 7 A, 10 A and 13 A
Thanks for this information, Mr Kenyon. I'm glad that British Standards now represents common practice.
I understand that in the early days of BS 1363 plugs, the official range of fuses available was 3 A, 7 A and 13 A, but this has been revised a few times.