Alan Capon:
Another thought, I f you look at the BSI website, you will find that previous versions of BS7671, for example BS7671:2008 + A3, are marked as “withdrawn”:
“Status : Superseded, Withdrawn Published : January 2015 Replaced By : BS 7671:2018+A1:2020”
UKPN:
"The 17th ed permitted the use of PME earthing systems to be connected............
This is the problem, the "wiring regulations" and its disciples and "experts" are so far down their own road they believe its the law. To say it can be referred to in court is like me saying to my neighbour you can drive at 50mph in our 30mph road. Its nothing to do with me, my opinion counts for nothing.
Its the ESQCR and HASWA which will be referred to.
Why the "wiring regulations" keep getting involved in DNO matters baffles me. I thought they got the message when the "improvement to the DNO network" fiasco was chucked out.
5 years on, they havent accounted for one of the other disasters the unearthed steel fuseboxes on TT. Its left to the manufacturers, DNO to advise the public.
The latest shambles? PME discon gadgets.
No, just look inside the front cover. You must use you own skill and judgement, (and abide by the law}
Mind how you go, UKPN
Interesting, then, why the ESQCR directly reference "British standard requirements" isn't it?
Yes, legislation is paramount in the considerations of consumers, duty holders, and DNOs, but ACOPs and British Standards have a place in the legislative framework too.
davezawadi (David Stone):
Except Mike, an RCD socket is not strictly permitted by BS7671, in that the standard is not recognised. You have replaced one deviation with another!
Not strictly true - the issue is just with BS 7288 style RCD sockets - other arrangements of RCD sockets which incorporate a BS EN 61008 device would be permitted - e.g.
https://www.ashleyelectrical.co.uk/56-series-13a-250v-1-gang-rcd-protection-without-enclosure-grey (or indeed a conventional socket RCD that complies with BS EN 61008 or 9 in addition to BS 7288)
- Andy.
John Peckham:
BS 7671 has no provisions for Deviations. There is a however the provision for a Departure. A Departure is a deliberate act, it has to be no less safe that the requirements of BS 7671 and has to be recorded on the installation certificate, see Regulation 120.3.
BS 7671 does not recognise BS 7288 devices for fault protection or additional protection see Regulations 531.3.4.1 and 531.3.4.2. BS 7288 devices in my view cannot be used for additional protection or isolation as in the standard they have to be protected by an upstream RCD. So they are less safe than the provisions of BS7671 and cannot be used as a Departure.
"A BS 7288 socket outlet is better than nothing": discuss.
Chris Pearson:John Peckham:
BS 7671 has no provisions for Deviations. There is a however the provision for a Departure. A Departure is a deliberate act, it has to be no less safe that the requirements of BS 7671 and has to be recorded on the installation certificate, see Regulation 120.3.
BS 7671 does not recognise BS 7288 devices for fault protection or additional protection see Regulations 531.3.4.1 and 531.3.4.2. BS 7288 devices in my view cannot be used for additional protection or isolation as in the standard they have to be protected by an upstream RCD. So they are less safe than the provisions of BS7671 and cannot be used as a Departure."A BS 7288 socket outlet is better than nothing": discuss.
Although I'd given up so to speak on this BS7671/ EWR contravention observation (or whatever it is) regarding minor works, on the 'better than nothing' question and still linking into 7671 minor works, then I'd answer with, suggesting perhaps... in some situations.
In a bedroom upstairs (context matters?) , where another socket is required not too far from another (or another light point), I can't see that it (or RCD, or AFDD or any future additional protection) is really required for such minor works to be certified... and as said and again, I'd prefer if BS7671 accounted for these types of situations in general (domestic, commercial etc) as 'departures' doesn't strictly allow it, so one simply cannot sign off to BS7671 if work does not comply fully. There should be no law broken in such cases and we believe none would be.. oooerrr... in a non-virtuous realistic assessment ... and what could go wrong in any case in such a situation to be more unsafe from other sockets or light points in the same location.
Done. :-)