Hi, my first post, I wondered if I could get some advice from the community regarding a failed EICR report and the subsequent remedial works.

Me letting agent appointed a local electrical firm to conduct an EICR report on my flat before new tenants moved in. The timescale was tight since the new tenants were due to move in on the 1st Feb.


The flat is a purpose-built flat constructed in 2005 so id be surprised if the electrics were too far out of spec.


The report came back as failed due to the following points:


1 No Bonding, substantial metal pipework in property

8 Fan is not low voltage in bathroom, and is in zone 2


the quotation for the remedial work was to install 100mm bonding from the consumer unit to the stop cock and replace the extractor with an extra low voltage fan and controller.

"estimate of a morning for 2 which hopefully will be less, however the route is not particularly easy" - £630 inc VAT.


the quote sounded high for a mornings work but due to time constraints i had to agree.


the final invoice came back as 28 hours work, £1399...  so that's 28 hours work to run about 6metres of earth bonding and replace the bathroom fan when the initial quote was a morning's work for £630.


So obviously I've questioned this and after doing some digging, I found that firstly 230v fans are allowed in zone 2, and not all incoming water pipes need to be bonded if there is plastic in the incoming supply..


I'll upload screenshots of the paper work and photos of the job, but any advice would be greatly appreciated!

fef58217ef06411ab3fcb5e012db7a01-huge-quotation.png



b2dc16ff7b1f285e61c95ea8dd664268-huge-eicr-report.png


  • davezawadi (David Stone):

    It is normally considered that a quotation is a contracted price. If you buy a new car, and you are quoted a price to compare with elsewhere do you expect to be charged more when you say yes? Certainly not.


    The devil is in the detail - it will all be in the small print somewhere. That is, of course, if there was a written contract.


    A quote may well be an offer: in other words, you offer to install MPBC and ELV for £630. If I accept the offer, there is a contract which is binding both ways.


    Concerning the new car, if a dealer offers to sell you a certain model for £15k and you refuse the offer with a view to shopping around, the offer expires. What happens next may be that you offer to buy the car for £15k, but the dealer is entitled to refuse and make a counter offer. Raising the price wouldn't make good business sense, but it might happen.


  • JoeB:
    Alcomax:

    Where is the supply fuse and electric meter in relation to the Flat?


    There is no gas you say, so is there off peak electric for heating and hot water or electric boiler and a 2nd consumer unit or maybe an extra large consumer unit with two sets of tails into it?


    this is what's inside the cupboard by the front door.  No gas, and night storage heaters and electric water heater. Economy7 electric. 
    754dc96bb785e257911979adc55848fa-original-image.png




    That's horrid! I like the fact that the tails have been tied together (although one appears to have slipped) but why not bring them into the bottom of the CU? Grommets would suffice on the bottom surface; glands would be even better.


  • It was sixteen years ago when it was installed, long before “tails glands” became in use.
  • Former Community Member
    0 Former Community Member
    Chris Pearson:
    JoeB:
    Alcomax:

    Where is the supply fuse and electric meter in relation to the Flat?


    There is no gas you say, so is there off peak electric for heating and hot water or electric boiler and a 2nd consumer unit or maybe an extra large consumer unit with two sets of tails into it?


    this is what's inside the cupboard by the front door.  No gas, and night storage heaters and electric water heater. Economy7 electric. 
    754dc96bb785e257911979adc55848fa-original-image.png




    That's horrid! I like the fact that the tails have been tied together (although one appears to have slipped) but why not bring them into the bottom of the CU? Grommets would suffice on the bottom surface; glands would be even better.




    Yeah it's not pretty is it.. 

    ​​​​​ haha


  • Zoomup:
    wallywombat:

    Note that zone height is measured from the "floor" of the bath or shower, not the floor of the bathroom.


    The pictures on page 244 of B.S. 7671 shows the 2.25 metre height as from the room floor. Fig. 701.2

    .




    So it does! (You learn something old every day.) Doesn't seem to make much sense though - zone 2 is really about what you can touch while sitting or standing in a bath or shower and if the base of the bath is higher, you can reach higher.


  • Agreed, years ago I pointed that one out to IEE as it was then. I suggested that if I had a bath on extended legs (not impossible) then heights for zones should be referenced from bath floor level rather than the floor the bath was sat on. But my point was not taken and room floor level won.

    PS if a fan is mounted on or below the ceiling then the height is to the bit of fan you can touch, not the ceiling its mounted under I would think
  • So basically is the fan wall or ceiling mounted? Is it actually in zone 2 if ceiling mounted. If it is in zone 2 is it of the correct IP rating for the zone. Would be good to see a photo of the whole board.
  • I see it’s ceiling mounted so highly unlikely to be in zone 2
  • Humm - that supply looks suspiciously like it might be CNE to the head (alternatively it might be split-con with L & N in one leg of the trouser and PE in the other, but I'm not convinced). CNE within a building isn't what the DNOs like to do these days (especially as they usually pass the buck to a fictional BNO) but was common enough a few years ago. The original design might then  have considered the block to consist of mutiple distinct installations with separate DNO supplies for each flat - and hence would have required main bonding (if necessary) within each flat (like a terrace of houses). If the water pipe is in contact with class I equipment in another installation (e.g. the pump - presumably on the landlord's supply) then it would be classed as an extraneous-conductive-part as far as the flat was concerned (even if the water originally came out of the ground in plastic). Just a thought...

       - Andy.
  • " and hence would have required main bonding (if necessary) within each flat (like a terrace of houses). If the water pipe is in contact with class I equipment in another installation (e.g. the pump - presumably on the landlord's supply) then it would be classed as an extraneous-conductive-part as far as the flat was concerned (even if the water originally came out of the ground in plastic). "


    If that was the case then it would never had got passed building control when first built?......