Should a time delayed 100mA type be used? The Guidance note says that the 100 mA R.C.D. is chosen to discriminate with the pitch socket outlets R.C.D.s
AJJewsbury:Should a time delayed 100mA type be used? The Guidance note says that the 100 mA R.C.D. is chosen to discriminate with the pitch socket outlets R.C.D.s
Yes - you always need timedelay on any upstream RCD to achieve discrimination - as Reg 536.4.1.4 etc. tries to say (but probably with far too many words).
To my mind the ratio of the residual ratings should ideally be 3:1 not to highest rated downstream device, but to the sum of the downstream devices.
- Andy.
So, the Fig. 7.1 illustration should have the words "Time delayed" added to the 100 mA R.C.D. that supplies 4 caravans, in Guidance Note 7, Special Locations.
Z.
Kelly Marie Angel:
What is actually tripping? You say there is a 30 mA RCD in the van and in the pitch hook up point is it both of these or just one? Or was it one of the MCBs? If it was then yes that points to an overload 16 amps seems a bit stingy and with a few electric heaters and suchlike its easy to exceed that. Finally where is this in the country I know of one caravan site that has big supply problems due to an undersized pole pig. Sorry zoomup I not trying to teach you how to do fault finding i could of worded it better
I suspect overloading myself on this Norfolk site. The customer can not remember exactly what tripped off, but all is reset and is on now. Some sites are downgrading to a 10 Amp. per pitch supply from the traditional 16 Amp. supply. The site electrics used to be purely for touring vans, but now are for statics. I wonder if the electrics have not been upgraded to allow for this as tourers usually demand less electricity, a battery charger, t.v., heater and a kettle maximum.
Z.
wallywombat:
I got lost around when you mentioned 100mA. Is this an existing device, or is it a proposal to install one to reduce nuisance tripping?
The 100mA R.C.D. supplies 4 individual pitches maximum, each with a 30mA R.C.D. per pitch. So up to 4 caravans run through one 100mA R.C.D.
Z.