EV charger on split load
Hi,
I am planning an EV charger install, and intended on using an RCBO directly off the main switch. The issue is that the board is MK, and I am unable to find a C40 with a type A rating for the RCD. I can only find a B40 with a type A, which is no good.
Installing a new board is not an option. I am however able to find a double pole 100A type A RCCB.
Albeit not ideal, is there anything “wrong” on face value with installing the EV onto an RCCB with other circuits (like ring mains). I fully appreciate it isn't ideal for the isolation of circuits should a fault appear, but to me this does provide suitable overload and RCD protection.
Any thoughts otherwise?
Thanks.
  • MK devices are back in production under licence.
  •  You could perhaps get a C40 MCB  (example) and put a double pole  RCD in a box nearer the charger ? I have a feeling the MK RCBOs are not neutral breaking. The symbol on the plastics suggests it is not.
  • Here’s what you are looking for, but not necessarily what you want and not guarantee by MK
    https://www.circpro.co.uk/mk-sentry-rcbo
  • You are correct re the non-disconnection of Neutral, and I have decided on a C40 MCB in the consumer unit, with an RCD Type A in an IP enclosure under the EV charger.
    Thanks.
    I wouldn't really want to share a 30 mA RCD between a car charger and other circuits - the car chargers can have a significant amount of earth leakage and some are quite close to the tripping threshold of a 30 mA RCD on their own. Add in just a few milliamps of leakage from other circuits and you would have nuisance tripping problems.
    A Renault Zoe for example leaks 10-12 mA to earth on a single phase charger as soon as the contactor closes. You certainly can't charge two of them on a single 30 mA RCD. Other cars may vary, but they likely all have a similar EMC filter with significant capacitance to earth.
  • vantech:
    How about testing it with the B40?  At the worst, it might trip on inrush .. very likely it won't have any trouble.  If you don't see it trip on a few ons and offs of charging, just keep it.  The only difference with the B curve is that it's a bit more enthusiastic to trip, i.e. it gives tighter protection.  [The advice is purely technical, on what would be a nice solution for safety, function and cost. I appreciate you might be forced for some reason to obey the letter of the manufacturer's instructions, in which case you should ignore this … though I confess I'd be interested to know if it does nuisance-trip a B40…]