27 amp MCBs

I have heard from a not very reliable source, that 27 amp MCBs are used in Australia.

As most of us know, 2.5mm twin with earth cable is good for 27 amps under optimum conditions. It was alleged that the 27 amp MCBs are to allow for electric cookers on 2.5mm.

A quick look on Amazon and fleabay failed to find any 27 amp MCBs which makes me a bit doubtful. 25 amp MCBs are available but not common, and 27 amps offers a very marginal gain in capacity.

  • I spoke to an electrician who worked in prisons and he said he had never seen so many unusual sizes of MCBs until he opened a board in a prison as they have very close circuit protection.

  • Botany Bay perhaps?

  • There’s oddities such as 9.17 amp MCBs

    https://uk.rs-online.com/web/p/mcbs/2103399

  • Used to see 7 amp in Zimbabwe, usually on military accommodation married quarters on the un metered incomer, 7 was yer lot, lights, hot water,no heating as such

  • Without space heating, 7 amps is fine.

    A 1 kw or 1.2 kw water heater, with a changeover switch to permit use of a kettle or toaster instead. 6 lamps, mixed wattages, a couple of fans and a radio would be fine with sensible use of the lights, not all on at once.

    Could probably supply a fridge if care was taken. A forty watt fluorescent lamp with power factor correction would give a better light than a 100 watt incandescent bulb.

  • AFAIR cooking was done on a paraffin or wood burner, these were new builds in the 90s

  • Single guys presumably were allowed 2 amps each with shared bathrooms, etc.

     

  • Sparkingchip: 
     

    There’s oddities such as 9.17 amp MCBs

    https://uk.rs-online.com/web/p/mcbs/2103399

    Looks to me like an ordinary 10A nominal device … but someone has copied the wrong number from the data sheet (9.17A is the rating for 40 degree ambient rather than the usual 30 degree).

       - Andy.

  • AJJewsbury: 
     

    Sparkingchip: 
     

    There’s oddities such as 9.17 amp MCBs

    https://uk.rs-online.com/web/p/mcbs/2103399

    Looks to me like an ordinary 10A nominal device … but someone has copied the wrong number from the data sheet (9.17A is the rating for 40 degree ambient rather than the usual 30 degree).

       - Andy.

    Annnnnnnnnnnd the image shows a 16 Amp device.

    Z.

  • Annnnnnnnnnnd the image shows a 16 Amp device.]

    Yes, unfortunately that's typical of RS - “image indicative of range” is what they usually say…

       - Andy.