good day folks
out of interest, if anyone has filled in the “rated time delay” entry on an EIC for a 61008 type-s RCD main switch, what was the value (presuming the standard has a set value/range) used and where from ?
regards
Habs
good day folks
out of interest, if anyone has filled in the “rated time delay” entry on an EIC for a 61008 type-s RCD main switch, what was the value (presuming the standard has a set value/range) used and where from ?
regards
Habs
psychicwarrior:
was it worth posting all that @zoom , to then type “who cares about the actual trip time” . :-)
My question that I was caring about, was in relation to the space on the EIC for "rated time delay" and it seems reasonable to conclude that it is not really intended for s-types - so in that respect it's sorted.
Oh yes.
Z.
If you take a modern earth leakage relay to bits, the delay is quite tightly defined either by a resistor capacitor time constant, or a micro-controllor counting clock cycles. Unless you have deep pockets it should be a scrap one, as putting it back together is hard. There are DIP switches or twiddle knobs to set it.
Inside an type S things are simpler, the early ones just had a mechanical damping on the latch pull-off coil, and trip time varied with the degree of over-current, but the modern ones are closer to the analogue earth leakage relay, in using an RC delay, albeit one defined by the economics of the 20% tolerance parts bin, and some electronics and an SCR to fire a fairly sturdy actuator solenoid, these have a less variable delay once you get comfortably above the trip threshold.
As noted
‘ Slower than the slowest instant trip model, and
Fast enough to limit shock duration to less than a heartbeat’
was the original intention, though of course never written that way, and the spec is wide enough to accommodate all types.
Mike.
AJJewsbury:
As long as it is slower than say 40mS
Perhaps because a 30mA RCD might take 150ms to trip at 100mA (according to table 3A) - it's only guaranteed to hit 40ms at 150mA.
- Andy.
I find that most of the R.C.D.s that I test trip off at about 22mS at 30mA trip test current.
Z.
I find that most of the R.C.D.s that I test trip off at about 22mS at 30mA trip test current.
Indeed - but that's not guaranteed. If you want reliable discrimination in all (non-faulty) cases then you need to consider the worst-case conditions rather than just the common ones.
- Andy.
missed the question.
The max non- actuation time for a given over current, is the longest pulse of that level of earth leakage over-current you might apply and be sure you can do so without the trip process ever starting - i.e. without ever passing the point of no return in de-latching. Note that you may be able to pass a larger current for a bit longer and even after the point of no return is reached may take quite a bit longer for the contacts to be actually open - hence the other figures.
So
a 100ma S type will not de-latch in 130msec at 100mA, but it may at any longer duration, and will always have de-latched and be open cct by 0.5 seconds at that fault current or higher
it will not de-latch in 60msec at 200mA, but it may at any longer duration, and will have both de-latched and be open cct within 200ms at that current or higher
it will not de-latch in 50msec at 500mA, but it may at any longer duration, and will definitely have both de-latched and be open cct within 150ms at that current or higher
the explanation under the table is poorly worded.
Mike.
AJJewsbury:
As long as it is slower than say 40mS
Perhaps because a 30mA RCD might take 150ms to trip at 100mA (according to table 3A) - it's only guaranteed to hit 40ms at 150mA.
- Andy.
I have yet to find a good working 30mA R.C.D. that trips at more than approx. 30mS even at 30mA test current. They all turn off well within 40mS even at 30mA test current.
I like the Wylex WRS80/2. They are extremely reliable and of very good build quality.
Z.