good day folks

 

out of interest, if anyone has filled in the “rated time delay” entry on an EIC for a 61008 type-s RCD main switch,  what was the value  (presuming the standard has a set value/range)  used and where from ?

 

regards

Habs

 

  • psychicwarrior: 
     

    was it worth posting  all that @zoom , to then type “who cares about the actual trip time” .  :-)

    My question that I was caring about, was in relation to the space on the EIC for "rated  time delay" and it seems reasonable to conclude that it is not really intended for s-types -  so in that respect it's sorted.

    Oh yes.

    Z.

  • If you take a modern earth leakage relay to bits, the delay is quite tightly defined either by a resistor capacitor time constant, or a micro-controllor counting clock cycles. Unless you have deep pockets it should  be a scrap one, as putting it back together is hard. There are DIP switches or twiddle knobs to set it.

    Inside  an type S things are simpler,  the early ones just had a mechanical damping on the latch pull-off coil, and trip time varied with the degree of over-current, but the modern ones are closer to the analogue earth leakage relay, in using an RC delay, albeit one defined by the economics of the 20% tolerance parts bin, and some electronics and an SCR to fire a fairly sturdy actuator solenoid, these have a less variable  delay  once you get comfortably above the trip threshold.

    As noted 

    ‘ Slower than the slowest instant trip model, and 
    Fast enough to limit shock duration to less than a heartbeat’ 

    was the original intention, though of course never written that way, and the spec is wide enough to accommodate all types.

    Mike.

  • As long as it is slower than say 40mS

    Perhaps because a 30mA RCD might take 150ms to trip at 100mA (according to table 3A) - it's only guaranteed to hit 40ms at 150mA.

      - Andy.

  • AJJewsbury: 
     

    As long as it is slower than say 40mS

    Perhaps because a 30mA RCD might take 150ms to trip at 100mA (according to table 3A) - it's only guaranteed to hit 40ms at 150mA.

      - Andy.

    I find that most of the R.C.D.s that I test trip off at about 22mS at 30mA trip test current.

    Z.

  • I find that most of the R.C.D.s that I test trip off at about 22mS at 30mA trip test current.

    Indeed - but that's not guaranteed. If you want reliable discrimination in all (non-faulty) cases then you need to consider the worst-case conditions rather than just the common ones.

       - Andy.

  • missed the question. 

    The max non- actuation time for a given over current, is the longest pulse of that level of earth leakage over-current you might apply and be sure you can do so without the trip process ever starting - i.e. without ever passing the point of no return in de-latching. Note that you may be able to pass a larger current for a bit longer and even after the point of no return is reached may take quite a bit longer  for the contacts to be actually open - hence the other figures.

     

    So 

    a 100ma S type  will not de-latch in 130msec at 100mA, but it may at any longer duration, and will always have de-latched and be open cct by 0.5 seconds at that fault current or higher

    it  will not de-latch in 60msec at 200mA, but it may at any longer duration, and will have both de-latched and be open cct within  200ms at that current or higher

    it will not de-latch in 50msec at 500mA, but it may at any longer duration, and will definitely have both de-latched and be open cct within  150ms at that current or higher

    the explanation under the table is poorly worded.

    Mike.

  • AJJewsbury: 
     

    As long as it is slower than say 40mS

    Perhaps because a 30mA RCD might take 150ms to trip at 100mA (according to table 3A) - it's only guaranteed to hit 40ms at 150mA.

      - Andy.

    I have yet to find a good working 30mA R.C.D. that trips at more than approx. 30mS even at 30mA test current. They all turn off well within 40mS even at 30mA test current.