I have been asked to replace the  existing damaged T&E switched supply to a light in a steel framed barn on a farm and extend the switched supply to two adjoining steel frame barns and put a flood light in each. 

The light supply and switch are in a nearby old brick built building, the main supply is three phase PME without any RCD protection and the barns are used to house cattle (approx 100) . The steel support posts (22) are set in concrete in holes dug into sandstone. The barn floors are concrete on sandstone and will have straw bedding on top which gets wet.

I am going to stick an RCD in the supply to the lights. TT ing the farm is not an option.

My quandary is what is the least risk option:

1- Ignore BS7671 and keep the metalwork isolated from the supply earth as at present due to the risk of step voltage in the event of a lost neutral. Recently a DNO contractor did manage to loose a phase while working on a supply pole, but the barn metalwork will be extraneous so not a compliant solution,

2- Treat the metalwork (22 support posts) as the TT earth with the risk of step voltage around the posts until the  RCD trips;

3- TT the barn lighting circuit with a separate earth. It will very very difficult  to get a Ra lower than the barn supports due to the sandstone around most of the farm so potential for step voltages again and problem of finding an accessible place away from animals;

4 Just bond everything to the PME earth, hope the number of posts reduces the step voltages around each to a low level and accept the risks, or

4 - Something else  I have not thought of ?

I would normally use SWA and there is a 8 metre catenary involved, can anyone  recommend a better alternative as it will be close to 30M across three barns. Even though I will be in a cage on a tele handler I am not keen on trying to install SWA along the roof beams over 20ft up if there is an easier option, I will be using girder clips to secure the cable.

  • Coming back to the touch voltage on TT-TN mixes, it is not the N-CPC impedance in the loop divisor, it is the DNO side electrodes, so relative to the local terra-firma the L voltage will dip, by the amount that the neutral/PEN gets pulled away from terra-firmw earth.

    Not perhaps in this case with several houses plumbing augmenting the DNO earthing of the neutral, but in many rural cases the DNO earth is not much better than the customer one, so during fault the L_N voltage does not depress, but if you have a 10 ohm electrode resitance and so does the DNO, the whole 3 phase triangle of voltages goes walkabout.

    I'm also for option 2 by the way, and it does not have to be SWA if it is visible route.

    Mike.

  •  

    I'm also for option 2 by the way, and it does not have to be SWA if it is visible route.

    Mike.

    I would prefer S.W.A. cable as it offers protection from rodents in the barn, with possible shock/fire risks.

    Z.

  • Zoomup: 
     

     

    I'm also for option 2 by the way, and it does not have to be SWA if it is visible route.

    Mike.

    I would prefer S.W.A. cable as it offers protection from rodents in the barn, with possible shock/fire risks.

    Z.

    The brick built barn wiring is almost all T&E neatly clipped direct to wooden joists! 

    “It wasn't me gov it was like that when I got here”.

    I trust the man in the tele handler and I will be getting his son to do most of the work installing the cables, leaving me to do the technical bits sticking the bits of wire together?. I am getting too old for hard work and I no longer like working at heights. I find that as I have got older I have become far more risk adverse. 

    Earlier this year my BIL, in his 50s,  fell off a short stepladder when one leg dropped into a mole run when he was cutting a hedge. He suffered ten broken ribs on one side with three of them broken twice, had a flail chest and was in serious danger of dying. He was put into an induced coma for over a week during which time he had an operation to plate the double broken ones together. It took about three months to recover but he still suffers from pain.

    It has made me much more cautious especially when people who have survived serious accidents usually start the description “I was only…”

     

     

  • kfh: 
     

    Zoomup: 
     

     

    I'm also for option 2 by the way, and it does not have to be SWA if it is visible route.

    Mike.

    I would prefer S.W.A. cable as it offers protection from rodents in the barn, with possible shock/fire risks.

    Z.

    The brick built barn wiring is almost all T&E neatly clipped direct to wooden joists! 

    “It wasn't me gov it was like that when I got here”.

    I trust the man in the tele handler and I will be getting his son to do most of the work installing the cables, leaving me to do the technical bits sticking the bits of wire together?. I am getting too old for hard work and I no longer like working at heights. I find that as I have got older I have become far more risk adverse. 

    Earlier this year my BIL, in his 50s,  fell off a short stepladder when one leg dropped into a mole run when he was cutting a hedge. He suffered ten broken ribs on one side with three of them broken twice, had a flail chest and was in serious danger of dying. He was put into an induced coma for over a week during which time he had an operation to plate the double broken ones together. It took about three months to recover but he still suffers from pain.

    It has made me much more cautious especially when people who have survived serious accidents usually start the description “I was only…”

     

     

    Educating experiences and wise words there.

    Z.

  • As Mike and Graham correctly pointed out, I'd ignored Rb in my examples above.

    That wasn't entirely accidental though. Ra (your electrode or posts (in parallel) resistance to Earth) and Rb (the source's electrode's resistance to Earth) are in series and so the voltage is indeed divided across both - so when an Earth fault current is flowing a  voltage will develop across the supply electrode and thus the voltage across Ra is thus reduced by the same amount - making the consumer's installation somewhat safer. It is however hard to put a safe value on Rb - it's maximum is normally 20 Ohms but is often far lower. On a system that supplies TN customers as well, the supply PE/PEN is very likely to be bonded to many extraneous-conductive-parts and PME electrodes which effectively reduces Rb to much much lower values - often well below 1 Ohm. Ignoring Rb (or rather presuming it's effectively zero) simply errs on the side of safety by working to the worst case.

       - Andy.