Standard DNO Fault Current - incompatible MCB rating
Hi , I have a question.....  A small office building requires a new distribution board local to a 100A TPN DNO cut-out however, in lieu of an existing EICR, the standard Prospective line fault current is 25kA (3 phase), 16kA (1 phase).  With the DB in close proximity to the DNO the OCPD for final circuits needs to be types ITRO of 25kA breaking capacity ...... which are not available.... How would you mitigate this risk?
Am I missing something...?
  • Use the function in Amtech for has upstream protection which will show you what the PFC is at a particular part of the installation.
  • BTW, the highest prospective fault current that I have have found at a 13 amp socket outlet. was about 20 Ka not actually in the substation, but immediately adjacent.
    400 amp circuit from substation, into customers main switchgear, this supplied sub-mains to different areas of the building, and a small fuseboard adjacent. Socket outlet on side of fuseboard.
  • A slight point of order.
    " courtesy of annexe ZB of BS EN 61439-3."
    Suggests the committee have it in their gift to save your circuit breaker ;-) Actually of course it is the raw physics of fuses melting that get faster as the fault current increases, vs mechanical breakers which kind of run out of steam at very high fault currents and stop getting faster. The upper limit to the let-through energy of the fuse, means that everything beyond it sees any really large fault currents cut off early - the fuse is a 'death or glory' defence against a fairly unlikely silver stake (zero resistance) type fault near the origin. (A true zero resistance fault has no heat,no flash and no bang, real ones do involve some voltage drop, as energy is dissipated throwing hot metal about)
    The authors of  the annex simply capture that idea, and translate it into rather dull regs-language, to hide what is really going on.
  • Where might we see this fault of negligible impedance, other than Mr Blackwell's golden spanner loop tester, on an installation where the source can deliver unlimited current without any voltage depression?
  • I just love BS88-3 (IEC ASTA certified. 60269-3) fuses. Rated at 80kA. Totally reliable and they can reliably disconnect within just one half cycle. Also the wee grains of sand quash the arc. A wonder to behold. And when they blow a new factory fresh one is installed. Again totally reliable, unused, unharmed and wonderful.
  • What I have done is set the worst case DNO supply characteristics as being at the Transformer and then modelled the cable to the distribution board... Line fault current now drops below the 16kA MCB rating.
    Splendid! But surely the situation is not so complicated that specialised software is required?
    Concerning proximity to a substation (be it the DNO's or a private one), I'd be most interested to know the Ze of our neighbour across the road right next door to the transformer, but I have never had the cheek to ask to measure it. Doubtless the main goes out into the street, along a few yards, and then back in as the service cable, so a U-shaped route, albeit a short 'un.
  • Exactly my point - real faults have resistance, much as real supply transformers and cables do, and they share the volts between them and pass the same amps - so the assumption the PSSC is the full off load  loop voltage divided by the L-N, LL loop resistance or the Zs is not really true, some of the voltage drop is across the fault .   It all conspires to reduce the damage done do circuit breakers etc. But the big damage reduction comes from the early cut-off of the fault current by the disappearance of the fuse into widely spaced blobs of metal.