Regarding "Emergency Switching Off,"  please provide examples of "One single action only." What is "One single action only?" What types of devices are suitable for such use allowing one single action only? 465.3.

Parents
  • I had the very same "discussion" many years ago with what I would call and over zealous NICEIC inspector who basically stated that unless its a push button then no other device was for "Emergency switching". Now my discussion was around a lever operated device i.e a firefighter/firemans switch. So what some people have said on this thread, you need to grab the lever then push it up, the spring pin then latches it off.

    Now , when I then showed him what the regs indicated but also the standard description, the definition indicated and emergency stop can be either a button, rod or lever operated device, so with that definition Im still waiting on that NICEIC inspector to draw me or show me an example of a lever operated device that you dont grab then push up or down?

    Too many people focussing on one single action, to me its not the single action of what your hand does its the single operating action of one electrical accessory that latches in the off position and isolates all forms of energy etc from the installation/equipment/machine.

    Also with possible flames licking my backside then me activating that device would be so fast it would be classed as one action!!

    Cheers GTB

  • Agreed, Regulation Groups 537.3 and 537.4 ought to help sort that out. 537.3.3 does sort of lead you down the e-stop route, although there is a complete separate standard for e-stops.

    Now , when I then showed him what the regs indicated but also the standard description, the definition indicated and emergency stop can be either a button, rod or lever operated device, so with that definition Im still waiting on that NICEIC inspector to draw me or show me an example of a lever operated device that you dont grab then push up or down?

    Agreed.

    to me its not the single action of what your hand does its the single operating action of one electrical accessory that latches in the off position and isolates all forms of energy etc from the installation/equipment/machine.

    Again, agreed ... BUT we need to be careful to limit that to the switch that the person presses, rather than the actuator that removes power, otherwise e-stops operating on drop-out contactors (to the e-stop standard BS EN ISO 13850, or per  BS 4163 Health and safety for design and technology in educational and similar establishments) wouldn't be permitted, which I think adds weight to your argument.

  • And grabbing the firefighter's pole to reach the 2.75m high fire fighters' switch involves more than one single action.

    Z.

  • Definition. "EMERGENCY SWITCHING OFF. Opening operation of a switching device intended to remove electric power from an electrical installation to avert or alleviate a hazardous situation."

    The switch is normally manually operated. It will not be automatic. So the action must be simple and singular. A "single action only". 465.3.

    "Too many people focussing on one single action, to me its not the single action of what your hand does its the single operating action of one electrical accessory that latches in the off position and isolates all forms of energy etc from the installation/equipment/machine."

    The first sentence of 465.3  deals with the mechanics/electrics of the switching device. The second sentence deals with the human intervention to actually operate the switching device.

    MCG 25A 2 Pole 230V Fireman's Switch IP65 (FMS 25/2) | CEF

    Z.

Reply
  • Definition. "EMERGENCY SWITCHING OFF. Opening operation of a switching device intended to remove electric power from an electrical installation to avert or alleviate a hazardous situation."

    The switch is normally manually operated. It will not be automatic. So the action must be simple and singular. A "single action only". 465.3.

    "Too many people focussing on one single action, to me its not the single action of what your hand does its the single operating action of one electrical accessory that latches in the off position and isolates all forms of energy etc from the installation/equipment/machine."

    The first sentence of 465.3  deals with the mechanics/electrics of the switching device. The second sentence deals with the human intervention to actually operate the switching device.