EICR - does bathroom lighting outside zone 2 need to conform with IP rating and additional rcd protection?

Hi, I have received an EICR certificate with 2 C2s on bathroom lighting 1) Bathroom lighting does not conform to IP rating (note the lighting outside the zone based on published zoning guidance (low voltage spot light) but inspector insisted on ignoring the zoning guidance) 2) Bathroom lighting circuit is not connected to an RCD also supplementary bonding is not visible. 

Questions- 1) Are the C2s legitimate? As a layman, I find it difficult to understand why the inspector insisted on ignoring the bathroom zoning regulation (my ceiling is actually higher than most of the newer flat) . 2) Also how do I find out whether there is supplemental bonding in the bathroom lighting circuit (nothing is visible outside) - does it really warrant a C2 if I cannot prove that there is supplemental bonding (the lighting in my bathroom is low voltage (I don’t know what is the voltage but it is very dim) and is located outside zone) . 3) If the C2s are legitimate, how can I fix the issue with minimal cost? 

many thanks for your time in advance.

  • I’m sorry if anyone gets offended along these discussions. I don’t know anything about electricals and am really thankful that people are kind enough to offer many insights to the issue I faced. This EICR inspector only spent 10-15 minutes at my flat but cost me a lot of time to get to the bottom of it!

    I’m not keen to risk tripping lights with power so I don’t plan to go down option that may lead me to that.

    Still getting quotes but so far I have been quoted £400-£500 for just getting another RCd into the fuse box and changing the lights into IP67 for 2 hours’ labour plus MWC. I don’t know if that is expected (some insists on getting another EICR for me others charged me £150 just for MWC alone). I think this is a bit too steep for me at this juncture. So will have to continue and see how it goes. 

  • Now you’re going to have to wash your mouth out with soap and water.

  • This discussion seems to be going round and round in circles.

    There are 5 circuits. Two of them supply one appliance. One radial with 9 lights. Two rings.

    There is plenty of choice of consumer units for under £100. (Or push the boat out and get one with surge-protection.)

    Half a day's labour.

    Stop faffing about and get the CU changed.

  • Swapping the RCD to be the main switch should be relatively easy, it would seem logical that the hob and heater will have double pole switches so if they cause the RCD to trip they can simply be switched off at their respective double pole switches and the RCD reset.

    A RCD as the main switch very rarely causes problems in a flat.

  • I had a house that was wired like that, the only disadvantage would be that if the RCD tripped you lose both lights  and power.  It didn't happen to me but I was always conscious of the possibility. 

    David

  • Can getting new RCD fitted into the box be done in 2 hours? Someone quoted me £200 for that (not sure with or without parts or vat - still awaiting for confirmation) - this is done through some portal matching tradesmen with clients (as I don’t have any contacts).. Thanks

  • Thanks - is this an easy task for the electrician? Sorry may be asking for the obvious but I really have no clue:)

  • Ditto to that one Sparkingchip

  • There is a RCD option that has not been discussed, so long as the incoming supply is fused at 80-amps or less move the 30 mA RCD across to replace the main switch and just use one busbar.

    Then Bob’s your Uncle and Fannie’s your Aunt; and all your problems regards RCD protection for cables concealed in walls and such like that have been missed off the EICR go away, leaving two RCD related observations, a recommendation to subdivide the installation and to upgrade to a Type A RCD.

    I did something very similar in a flat for a family member who wanted to rent it out, the was a main switch consumer unit with the only RCD protection for around fifteen circuits being a RCBO on the socket circuit, the CU has a steel enclosure and is perfectly serviceable, so I swapped the main switch for a 30 mA RCD and the RCBO for a MCB, knowing if there were RCD tripping issues I would be the person getting phone calls late at night or weekends.

  • Thanks for the advice!