Temporary Connection of Generator to Domestic Distribution System

Hi All,

I recently came across a very interesting article - link below:

https://electrical.theiet.org/wiring-matters/years/2020/82-september-2020/mythbusters-6/

Where I find this article very interesting, is in relation to the requirement / or potentially non-requirement  of an Earth Spike, for the Temporary connection of a Generator to a building (in the article a Site Office is mentioned).

Please refer to the attached rough sketch / scheme for the Temporary Connection of Generator to Domestic Distribution System, which was originally based upon Figure 4 from the linked article - I wonder whether this could be considered, at least in principle, to be an appropriate proposal for the temporary connection of a generator to a domestic premises? In the attached scheme, there is no Earth Spike, and a 30mA RCD is included at the output of the generator, which would be connected to the generator via an appropriately sized SWA Cable. I would consider the potential for some nuisance tripping of the upstream 30mA RCD (in reality, this would be a rare occurrence) to be an acceptable price to pay, for the added protection that it would provide.

I would very much appreciate, if any of you could possibly find a moment or two, in order to share your thoughts in relation to the above / attached.

Thanks,

Harry G.


Parents
  • The SWA before the generator's RCD looks a little odd to me - usually SWA is chosen because of risk of mechanical damage and the usual mechanism is to earth the armour and use ADS to provide shock protection.

    Sorry for only spotting this a bit late and butting in.

    The reason for this (as recommended for one of the options for wiring systems in BS 7430) is clear if you think about a fault scenario of a severed cable. The generator can continue to run, but the protective conductor (providing connection to Earth, i.e. terra-firma itself) could well be broken. SWA is provided to help provide more mechanical protection, and increase the chance that, in a cable impact scenario between generator and installation, that the protective device at the generator will operate.

    I would, however, be inclined to put the RCD as close as possible to the generator because of the above scenario, and that is what we usually see on temporary power systems to BS 7909

  • Hi Graham,

    Thanks for your informative reply above.

    I put this project aside over the festive period, and have only just got around to picking it up again.

    We are now thinking that we may go with the arrangement shown in the attached picture.

    As regards the Earth Rod at the MET: I believe that this is a firm requirement (as per the Regs),when connecting a switched alternative power source?

    Correct me if I'm wrong though - with this set-up, in reality, it is very unlikely that a fault could occur between Gen L1 and True Earth, as the Gen Frame is bonded to Gen L2 and also to all local Exposed and Extraneous Conductive Parts.

    What  am trying to say is, it is difficult to see how any contact could be made between Gen L1 and Earth, other than via the Gen Frame, which is already bonded to Gen L2.

    As always, any feedback would be much appreciated.

    Mark G. 

  • What  am trying to say is, it is difficult to see how any contact could be made between Gen L1 and Earth, other than via the Gen Frame, which is already bonded to Gen L2.

    I think it's more the fact that if you connect the generator with, say, an insulated and sheathed cable, rather than SWA or similar, the fault is more likely to occur in the connecting cable ... and if the cpc in that cable is broken, the generator is not Earthed, and what comes next is more difficult to ascertain.

    Where non-SWA cables are used, the use of RCD at the generator itself is imperative ... where a wiring system with metallic protection connected to the grame and neutral is used, risks are much less.

  • Hi Graham,

    Thanks for your informative answer. 

    I think that we will look at using armoured cable between the RCBO and the 32A Wall Mounted Plug - with the armour connected to the Earth Terminal in the RCBO Enclosure.

    There will be a short run of H07RN-F (appx. 1m) between the Gen 32A Socket and the RCBO Enclosure - the latter being a robust plastic enclosure, mounted on the generator frame.

    As regards the Earth Rod, I guess there will be no getting around this, as it seems to be called-for in the Regs, for Switched Alternative Power Sources?

    Best Regards,

    Mark G.

  • it has to be for any emergency genset that may run with the street main in a fault state - part of that fault may be that the cable is cut and there is no earth at all, so for ADS reasons you need bring your own.
    Mike.

Reply
  • it has to be for any emergency genset that may run with the street main in a fault state - part of that fault may be that the cable is cut and there is no earth at all, so for ADS reasons you need bring your own.
    Mike.