Temporary Connection of Generator to Domestic Distribution System
Hi All,
I recently came across a very interesting article - link below:
https://electrical.theiet.org/wiring-matters/years/2020/82-september-2020/mythbusters-6/
Where I find this article very interesting, is in relation to the requirement / or potentially non-requirement  of an Earth Spike, for the Temporary connection of a Generator to a building (in the article a Site Office is mentioned).
Please refer to the attached rough sketch / scheme for the Temporary Connection of Generator to Domestic Distribution System, which was originally based upon Figure 4 from the linked article - I wonder whether this could be considered, at least in principle, to be an appropriate proposal for the temporary connection of a generator to a domestic premises? In the attached scheme, there is no Earth Spike, and a 30mA RCD is included at the output of the generator, which would be connected to the generator via an appropriately sized SWA Cable. I would consider the potential for some nuisance tripping of the upstream 30mA RCD (in reality, this would be a rare occurrence) to be an acceptable price to pay, for the added protection that it would provide.
I would very much appreciate, if any of you could possibly find a moment or two, in order to share your thoughts in relation to the above / attached.
Thanks,
Harry G.
  • As in a rough Restricted Earth Fault scheme built out of RCDs?
    (So would need care with, for example, saturation of CTs during out of zone faults, inrush harmonics etc)
    To avoid a loss of cover over the N-E link, one could also conceive the RCD being *downstream* of the link, but that’d need a 5P RCD (earth in a reverse direction) or more realistically an earth fault relay with all conductors going through a common toroidal/window CT at which point you might as well have a traditional REF.
  • An RCD before the N-E link never trips for any sort of fault to earth, between RCD and and the link, as it just looks like an additional load.    You may want breaking at that point you probably want the sensing that drives it somewhere else.
    Yup - but that's just the same as for faults between the N-PE link and RCD in a conventional TN-S system - if the link and RCD(s) are close together (especially if in the same enclosure) I reckon the risks can be mitigated with a bit of care in layout and/or additional sheathing to meet double/reinforced insulation approach.
  • Well as I thought would happen.
    Soon as the geny. was fired up and either of 2 manual change over switches were operated to connect a load to the geny. the RCD tripped.
    Stephill actually supplied a 100mA ( non adjustable type ) with this particular generator.
    Of course the customer immediately said...well it was alright with the old 6kVa petrol geny; without any RCD protection of course, which helped me no end.
    Monday is going to bring a busy day chasing for earth leakage!.
    Only 2 of the 6 installations this generator supplies have any form of ( 30mA ) RCD protection so I'll start with those installations that haven't,
    .Could be a long old day!