Good morning Guys,
I refer to Chapter 52 ( 521.9) of BS 7671, Can we use class 5 conductor ( multicore Cable) in fixed Installation for wiring lighting, power ? Grateful if someone can help answer with document evidence.
The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement
Good morning Guys,
I refer to Chapter 52 ( 521.9) of BS 7671, Can we use class 5 conductor ( multicore Cable) in fixed Installation for wiring lighting, power ? Grateful if someone can help answer with document evidence.
As in the Regulation, if the cable is protected against damage, then it is fine to be used.
Multiple inset downlights use flex, as, basically, the connection blocks for them do not have enough room for 2x 1.5mm T+E cables, so a JB, and a flex off to the fitting is the usual solution.
As in the Regulation, if the cable is protected against damage, then it is fine to be used.
Multiple inset downlights use flex, as, basically, the connection blocks for them do not have enough room for 2x 1.5mm T+E cables, so a JB, and a flex off to the fitting is the usual solution.