How are hand wires in toilets wired up?
So how are hand dryers usually wired in a radial circuit?
Is the supply cable from consumer board connected to supply side of a FCU and then the load side connected to wago connectors (L and N have their own connectors). Then hand dryer connected to the wago connectors. Then a second FCU is connected to the wago connector and the load side of second FCU  connected to the Hand dryer.
Thanks.
  • In terms of both potential abuse/vandalism and consequent liability, wet skin in public toilets are probably higher risk to the installation owner than say a private domestic kitchen.
  • The installation owner probably seldom visits the premises, but I think that I know what you mean.
    I find it hard to believe that using a plug and socket would (could even) give rise to a claim in tort.
    Returning to the original question, there is nothing complicated: I'd opt for a 4 mm² radial to FCUs.
  • Sorry - I reading my reply again I realise I wasn't that clear - what I was trying to say was than public toilets often suffer a higher level of abuse/vandalism/damage - so the designer might well think it appropriate to take additional precautions over and above general BS 7671 requirements, in order to protect whoever the user happens to be from electrical harm and installation owner from the consequential legal liabilities. You can imagine a lawyer was it really reasonable in the circumstances to omit 30mA RCD additional protection (even if BS 7671 permits that in the general case) or make available a 13A socket available to plug in a phone charger in such an environment.
  • You can imagine a lawyer was it really reasonable in the circumstances to omit 30mA RCD additional protection
    If I can remember tomorrow, I shall see if I can find out whether the hand driers in the courts have RCD protection. The sparks was in last week so he might still be there on Monday.
  • So kind of like this? The incoming supply is looped in.
    Earthing isn't shown.
  • That is fine for multiple dryers ( which isn't clear in your first post ) so long as the supply cable and circuit breaker are large enough to feed 2 dryers. You may have a little leaway if the dryers are not used too much at the same time.
    Gary
  • The sparks was in today and no, the courts in which I sit do not have RCD protection on the hand-drier circuits, so that answers Andy's point. :-)
    He told me that he was changing a florrie in another court building once. He had poked his head above the false ceiling and unplugged the lamp fitting at which point he got a belt off the plug. It turned out that somebody had "borrowed" a neutral from the lamp fitting.
    My conclusion is that it may be safest to use paper towels from now on.