Touch voltage

Hello

I have a basic question on touch voltage. I just can't seem to grasp it..
This is taken from guidance note 5
I have attached 3 sketches alongside .

1 and 2 are as GN5 describes

The third is my confusion.

1 & 2. We calculated touch voltage, in this case 126V without MPB and 94V with MPB

Now I understand I think the basic concept the greater the resistance , the higher the voltage current being constant

Number 3, is How I imagine it...
We have a fault and at the Exposed CP we have a voltage of say 115V
The resistance of the CPC to the MET will reduce this voltage again to say half again so 57.5V at the MET

Since we have MPB connected to the MET . The MET and Extraneous part will be  roughly at 57.5V

So our touch voltage would be between the EXP and EXT conductive part so.115V   ----   57.5V   A difference of  57.5V

I don't understand in the GN5 examples, Why is  touch voltage is one amount?
126 volts to what?  To Earth? 
But since the MET will be at a raised potential It can't be to earth?

Hope that makes sense.


Parents
  • This is really helpful thank you. I promise not to keep bothering you.


    Just on the Supplementary though..

    So Ut = If (in SB) x 0.05

    the supplementary bond is in effect parallel with the c.p.c - which reduces the overall earth fault loop impedance, and so increases the fault current

    So calculation of the  new Zs is needed

     253V

    0.05Ω SB and 0.5Ω R2 in parallel = 0.05Ω

    plus R1 0.5

    + Ze 0.35Ω

    Zs 0.5+0.05+0.35 =0.9

    253 / 0.9 = 281.1A

    281 x 0.05 = 14.05V

    So without bonding we had  Ut = 126.5V
    With bonding Ut = 93.7V

    With Supplementary  = 14.05V?

    Thank you




  • Nearly -

    With a fault current of 281.1A flowing through the CPC of 0.5Ω and SB/pipe/MEB of  0.05Ω (say negligible for pipe and MEB) then 90% of the fault current will flow through the SB; i.e. 253A.

    So Ut = 253 x 0.05 = 12.65V

Reply
  • Nearly -

    With a fault current of 281.1A flowing through the CPC of 0.5Ω and SB/pipe/MEB of  0.05Ω (say negligible for pipe and MEB) then 90% of the fault current will flow through the SB; i.e. 253A.

    So Ut = 253 x 0.05 = 12.65V