Touch voltage

Hello

I have a basic question on touch voltage. I just can't seem to grasp it..
This is taken from guidance note 5
I have attached 3 sketches alongside .

1 and 2 are as GN5 describes

The third is my confusion.

1 & 2. We calculated touch voltage, in this case 126V without MPB and 94V with MPB

Now I understand I think the basic concept the greater the resistance , the higher the voltage current being constant

Number 3, is How I imagine it...
We have a fault and at the Exposed CP we have a voltage of say 115V
The resistance of the CPC to the MET will reduce this voltage again to say half again so 57.5V at the MET

Since we have MPB connected to the MET . The MET and Extraneous part will be  roughly at 57.5V

So our touch voltage would be between the EXP and EXT conductive part so.115V   ----   57.5V   A difference of  57.5V

I don't understand in the GN5 examples, Why is  touch voltage is one amount?
126 volts to what?  To Earth? 
But since the MET will be at a raised potential It can't be to earth?

Hope that makes sense.


  • No, I disagree with the 'supplementary bond is in effect parallel with the cpc' in all cases.

    I don't disagree with your disagreement, but would point out I was merely suggesting an approach that would allow calculation of values for the particular example under consideration.

       - Andy.

  • If this exposed to extraneous-c-p resistance happens to be 1.5Ω on a 6A circuit where R<50/Ia is 1.67Ω,

    how does that have any bearing on touch voltage?

    In the worst case condition where practically all the earth fault current follows the same path as your 1.5Ω measurement, a voltage difference of 50V won't persist for longer than 5s.

    Also where conventional overcurrent devices are used for ADS, where the fault current exceeds what would generate 50V, the disconnection time would be correspondingly reduced - given the characteristics of most devices, that's likely to be on a curve that would meet 0.4s if the current could generate 115V and 0.2 for 230V.  So it's a kind of sliding scale ADS if you like - at the top end it's pretty much like ordinary ADS, but as the fault currents and hence voltage differences drop, longer disconnection times are permitted, until we get down to 50V at which point disconnection (for shock protection at least) isn't needed at all. (Although in most cases you'd still want to disconnect an earth fault fairly promptly to avoid overheating or fire risks).

       - Andy.