Touch voltage

Hello

I have a basic question on touch voltage. I just can't seem to grasp it..
This is taken from guidance note 5
I have attached 3 sketches alongside .

1 and 2 are as GN5 describes

The third is my confusion.

1 & 2. We calculated touch voltage, in this case 126V without MPB and 94V with MPB

Now I understand I think the basic concept the greater the resistance , the higher the voltage current being constant

Number 3, is How I imagine it...
We have a fault and at the Exposed CP we have a voltage of say 115V
The resistance of the CPC to the MET will reduce this voltage again to say half again so 57.5V at the MET

Since we have MPB connected to the MET . The MET and Extraneous part will be  roughly at 57.5V

So our touch voltage would be between the EXP and EXT conductive part so.115V   ----   57.5V   A difference of  57.5V

I don't understand in the GN5 examples, Why is  touch voltage is one amount?
126 volts to what?  To Earth? 
But since the MET will be at a raised potential It can't be to earth?

Hope that makes sense.


Parents
  • This is really helpful thank you. I promise not to keep bothering you.


    Just on the Supplementary though..

    So Ut = If (in SB) x 0.05

    the supplementary bond is in effect parallel with the c.p.c - which reduces the overall earth fault loop impedance, and so increases the fault current

    So calculation of the  new Zs is needed

     253V

    0.05Ω SB and 0.5Ω R2 in parallel = 0.05Ω

    plus R1 0.5

    + Ze 0.35Ω

    Zs 0.5+0.05+0.35 =0.9

    253 / 0.9 = 281.1A

    281 x 0.05 = 14.05V

    So without bonding we had  Ut = 126.5V
    With bonding Ut = 93.7V

    With Supplementary  = 14.05V?

    Thank you




  • Nearly -

    With a fault current of 281.1A flowing through the CPC of 0.5Ω and SB/pipe/MEB of  0.05Ω (say negligible for pipe and MEB) then 90% of the fault current will flow through the SB; i.e. 253A.

    So Ut = 253 x 0.05 = 12.65V

  • Just on the Supplementary though..

    So Ut = If (in SB) x 0.05

    the supplementary bond is in effect parallel with the c.p.c - which reduces the overall earth fault loop impedance, and so increases the fault current

    No, I disagree with the 'supplementary bond is in effect parallel with the cpc' in all cases. The resistance cpc's of the circuits alone (R2 of circuit 1 + R2 of circuit 2) may be of sufficiently low resistance to a common DB earth terminal (or in a smaller installation, all the way back to MET) to meet the requirements of Regulation 415.2, especially if RCDs are used. And, see 544.2.1, protective conductors in sheathed cables, or in conduit or trunking, mean the minimum csa can be less than 4 sq mm; the only issue is if there's a disparity in cpc csa between the circuits ... you'd have to reinforce the smaller one with a conductor of csa not less than the largest of the cpc's.

    Also, highlights the fact that 415.2 does not necessarily reduce touch-voltage. It 'reduces touch-voltage to 50 V AC or 120 V DC or less for currents that will not operate the relevant overcurrent protective device in 5 s, or alternatively the relevant RCD in either 0.3 s (for non time-delayed devices) or 0.5 s (for S time-delay devices).'

    If the fault current is more than Ia, the touch-voltage may well be > (or even >>) 50 V AC or 120 V DC, but will be disconnected in a known time.

    Look closely at the formulae in 415.2.2:

    415.2.2 The resistance R between simultaneously accessible exposed-conductive-parts and extraneous-conductive-parts shall fulfil the following condition:

    R ≤ 50 V/Ia in AC systems

    R ≤ 120 V/Ia in DC systems

    where Ia is the operating current in amperes (A) of the protective device or:

    (i) for RCDs, IΔn

    (ii) for overcurrent devices, the 5 s operating current.

    Nothing in BS 7671 limits touch-voltages absolutely in all possible fault conditions, except SELV (and even then, caution if you choose certain modern electronic sources, because they don't all conform to 414.1.1 with respect to voltage limits in certain Sections in Part 7).

  • If this exposed to extraneous-c-p resistance happens to be 1.5Ω on a 6A circuit where R<50/Ia is 1.67Ω,

    how does that have any bearing on touch voltage?

  • No, I disagree with the 'supplementary bond is in effect parallel with the cpc' in all cases.

    I don't disagree with your disagreement, but would point out I was merely suggesting an approach that would allow calculation of values for the particular example under consideration.

       - Andy.

  • If this exposed to extraneous-c-p resistance happens to be 1.5Ω on a 6A circuit where R<50/Ia is 1.67Ω,

    how does that have any bearing on touch voltage?

    In the worst case condition where practically all the earth fault current follows the same path as your 1.5Ω measurement, a voltage difference of 50V won't persist for longer than 5s.

    Also where conventional overcurrent devices are used for ADS, where the fault current exceeds what would generate 50V, the disconnection time would be correspondingly reduced - given the characteristics of most devices, that's likely to be on a curve that would meet 0.4s if the current could generate 115V and 0.2 for 230V.  So it's a kind of sliding scale ADS if you like - at the top end it's pretty much like ordinary ADS, but as the fault currents and hence voltage differences drop, longer disconnection times are permitted, until we get down to 50V at which point disconnection (for shock protection at least) isn't needed at all. (Although in most cases you'd still want to disconnect an earth fault fairly promptly to avoid overheating or fire risks).

       - Andy.

Reply
  • If this exposed to extraneous-c-p resistance happens to be 1.5Ω on a 6A circuit where R<50/Ia is 1.67Ω,

    how does that have any bearing on touch voltage?

    In the worst case condition where practically all the earth fault current follows the same path as your 1.5Ω measurement, a voltage difference of 50V won't persist for longer than 5s.

    Also where conventional overcurrent devices are used for ADS, where the fault current exceeds what would generate 50V, the disconnection time would be correspondingly reduced - given the characteristics of most devices, that's likely to be on a curve that would meet 0.4s if the current could generate 115V and 0.2 for 230V.  So it's a kind of sliding scale ADS if you like - at the top end it's pretty much like ordinary ADS, but as the fault currents and hence voltage differences drop, longer disconnection times are permitted, until we get down to 50V at which point disconnection (for shock protection at least) isn't needed at all. (Although in most cases you'd still want to disconnect an earth fault fairly promptly to avoid overheating or fire risks).

       - Andy.

Children
No Data