DNO Residential Supply Main Cutout Fuses and Potential Fault Current (PFC)
There seems to be a lot of emphasis on recording the highest value of PFC being less than the protective devises can safely handle, but little or no reference to when the pfc might be too low to operate the device in the prescribed time. In fact, most installation and inspection certificates simple note the device manufacturers maximum safe fault current, giving the electrician an excuse perhaps to not even measure the pfc!
I’m long retired but investigating a potentially serious electrical fire for a friend, though fortunately, this time, no fatalities as it was confined to a detached intake cabinet well away from the building. Which brings me to another point, the ESQC Regulations stress reporting an incident to the Secretary of State if any fatalities, but no such requirement if none (this time!). Sadly, a missed opportunity perhaps to reduce the risk of similar failures causing fatalities in future.
Anyway, for now, back to the pfc issue: In their case they had very recently had a 3 phase upgrade to their large property, with DNO 100amp cutout fuses (BS1361 or similar). The supply service cable serves several properties, with theirs being near the end of the supply service cable. Both the calculated pfc and measured value indicate around half the pfc required to operate the cutout fuses in the prescribed time, and in the event, persisted in the fault mode (apparently faulty meter or loose meter connection) for perhaps in excess of 15 minutes, further aiding the developing fire. Currently, their loads are all single phase and shared across the 3 phases, with ample capacity for future load additions.
So 2 questions if I may, one around the related ESQC regulations notification issue, and one about no obvious provision for recording a measured value of pfc on certificates, and no obvious requirement on the certificate to act accordingly when the measured pfc is too low.
  • yes, well if it was a cast iron gas main or a water pipe of that vintage, it would have been renewed as a length back to the TX by now, and any house wiring of that age would be getting the sucking of teeth "needs a rewire missus" treatment - but  DNOs don't think like that.
  • to get around the PMS 0.35ohm limit
    The old 0.35Ω for PME and 0.8Ω for TN-S limits no longer apply (since P23/1 has been replaced by P23/2) - they now only say that "90% of premises will have an EFLI below 0.34Ω" - so if you're in the unfortunate other 10% it can be higher.
    https://electrical.theiet.org/wiring-matters/years/2018/72-september-2018/earth-fault-loop-impedance-revision-of-ena-engineering-recommendation-p23/
  • well that suggests that most of the 0,45 ohms is not the new short length of 3 core to the property boundary, but the longer length of slightly fatter stuff back to the transformer.
  • Ha A picture tells a thousand words!
    Apart from the non standard colours of all the cables now being carbon black there are a few more serious observations.
    1) The DNO cut-out looks fine, there is no evidence of the incoming cable overheating or even being damage by this experience. Amusing it is thinner than the SWA leaving on the customer side. Probably 35mm2 for 100A supply.
    2) That's a "bog standard" TNCs head (Probably the 3 phase model in the series 8  it certainly has the rounded lower part and the modular look., ) and it looks very much like it has  an electrode wire.
    3) The customer box of fuses (and RCD ?) and outbound cable show no signs of distress. Apart from being externally covered in soot of course..
    It's a clear case of a meter fire and to be honest, if there was a high resistance joint in or at the connection to the  meter that could have happened just as easily at 5 amps as it could happen at 50 - you only need a few tens of watts to start a decent fire, there may well have been no overload of the supply at all to cause that, just a few extra volts drop at a few tens of amps.
    I presume the building lights flickered a bit, and then smoke was noticed ?
    Unless some one else had touched it, it should be squarely the responsibility of the metering company and or their installers.
    Not sure that any AFD would be guaranteed to  help unless it was upstream of the meter.
    Edit with a 400A PSSC, a dead short, L-N or LE would probably get the power off in about ten seconds, so not that long.
  • They only upgraded because the contract stated 100 amps per phase
    With all due respect, I very much doubt it. There are 100 A fuses in my TP service head, but my contract is for after diversity maximum demand of 30 kVA.
    Given that your friend's supply does not seem to be particularly robust, I would be surprised if the DNO permitted the full 69 kVA.
  • Yes, lights flickered for quite some time before the power failed, perhaps in excess of 15 mins apparently. Two of the 100 amp fuses blew, though so far, I don't know which one survived. Interestingly, the neutral out of the meter to me, shows signs of excessive overheating, though I'm still thinking about that one as beyond the isolator, it looks quite healthy, but the connection may well have been loose as it seems it could have blown away from the meter terminal, so yes, I agree, metering company or their installers, and we are waiting for them to respond. It could be that the house circuit was on the surviving fuse, and powered the lights well after the other two fuses blew, until the neutral blew clear from the meter terminal. As for the fuse characteristics, in my haste, I must have read the logarithmic scale wrongly. Here's a photo of the cubicle before they reverted to "TNS":
  • That first "isolator" really gets up my nose! Rage
    I do not see the purpose of the fuses in the switch-fuse (assuming that there are not solid links), but you have a perfectly decent big boy's means of isolation so why fit another one? What you have is 8 more potentially loose connections.
    I had exactly this, but refused point blank to let them fit one. Once my isolator is off, it stays off and can be fitted with a proper padlock and not just one of those flimsy dolly things.
    Why has the armour of the SWA been reinforced with the green and yellow please?
  • arguably on a system with inadequate ability to clear a line to earth fault, it is the big metal clad switch that is out of proportion and more dangerous under a fault condition due to its metal case being at half mains voltage.
    Certainly if the company fuses and the ones in the metal box are the same rating, but only the DNO ones failed, then the problem is in the meter, but the fuse current is only exceeded probably  right at the end of the event -  well in the last ten seconds - when two phases were fairly solidly bridged, either as the live metal moved through the plastic like a hot wire cutter, or because the build up of conductive char formed a phase to phase bridge.
    Phase to phase we may expect a rather higher PSSC of course - perhaps more like 600A, or more like 900 on an all 3  phases fault. Either could stop after blowing 2/3 fuses.
  • Thanks Chris,I've only been on site once, just before recent holiday, long enough to take a few more photos to aid me knocking up a block schematic of the load side, for when I got home (last week). I've not yet seen inside the new cabinet (or the interlocked old one), but I asked him to fit the extra fuses (63amp BS88-3's) before I went away, really as a temporary safety measure, to minimise risk of a further fire whilst on holiday. So at the time of fire, it relied on the company fuses, and I agree, the phase to phase is apparently nearer likely nearer 800 amps as you say. I also hate the interlocked isolator, my pet hate when in industry, especially inside a locked cabinet. I'm still trying to find out what company fuse survived the fire, particularly as the neutral appears open circuit at that stage, and may well have livened up the isolator, but hopefully, the specialists on site post fire checked all that before touching it. For my only visit, so far, the installation was up and running again, but yet another interlocked door (plastic isolator this time), so I've not seen inside it yet as did not want to power off the household while they were offsite. I hope to get back later this week. Company fuses are 100 Amp.
  • I agree, and asked their electrician why he fitted the extra isolator (interlocked with door) when I first saw it, (the post fire one) particularly as it was all inside the main locked cabinet, and he said that it was due to the need for an isolator in the reg's as distribution board was around 10 metres away,  ie, over 3 metres, though I've yet to double check BS7671 on this as personally, I'm happy with just the company isolator.