Is this junction box installation acceptable?

This junction box has been installed by my builder's electrical worker, the void above the box is the ceiling space on ground floor

is this acceptable for residential installation?

  • Presumably the cables were too short, or whatever was origianlly there has been moved? Its looks a decent enough install to me, far better than all the cables twisted togther in a standard box.

  • Is there a lid that you have removed to take the picture ?  the terminals should not be accessible without the use of tools so it needs a lid.

    Are the cables likely to be pulled ?- presumably not if they are part of a fixed installation but if they are they should be clipped somewhere - that could be to the joist in the space above.

    There may be questions about cable ratings and grouping factors, but it is stripped back to singles that are well spaced, so that has presumably been considered but worth noting.

    Something like this - a DIN box and a row of terminals, is what often happens when a consumer unit has to be relocated and every circuit needs to be a few metres longer.

    In ideal land,  might have liked to see some glanding or cable grip at the top of the box where the cables exit but with the lid on it could be a lot worse - you could have found those terminal blocks just flapping in the breeze in the floor-ceiling void.

    The hole in the box seems to have been chewed out, rather than neatly cut, and the use of spray foam is a bit 'rough'. but that is not a breach of regs.

    The terminals are full insulated so as long as the wires are fully seated, i.e. no copper showing, the hole in the outer box on its own is not a safety concern, as even if you could poke a finger in there is nothing for it to  hit that is live - so it meets IPXXB (jointed fingers) and  IPXXD (1mm spike probe) as well. That is before you add the floor above, that I presume needs tools to remove?

    Is there some specific aspect that especially concerns you?

    regards

    Mike.

  • looks neat enough would suggest grommet strip and fire sealing the entrance to the enclosure. Labelling the enclosure and cables for future maintenance would be a nice touch. 

  • Personally I don't like the large hole at the top - far too easy for dust, dirt, grit and all the other detritus that seems to magically appear in floor voids, to fall down into the innards - and I suspect lever terminals will be less tolerant of that than traditional screw ones.But technically it's not an accessible top surface so no automatic IP4X requirement. You could argue about it not being suitable for the conditions, but it's a vague requirement rather than something black and white you can point to - any there are many other much worse examples out there that seem to prove themselves adequate enough. There's also a hint of unsheathed cables outside of the enclosure, but that might be the camera angle...

       - Andy.

  • Is somebody going to push down that half-open green lever?

  • Good spot!

    The lever seems to be broken in the triplet left of it, but cpc and N: where is the line?

    (Presumably, there was a CU up against the ceiling at one time.)

  • Thanks all for your input.

    This is not the result of any equipment being moved, it is a collection of new lighting circuits in an extension that have been grouped together for connection in a central point. This box has been presented supplementary to all the hidden connections in the ceiling that were used to modify the existing circuits.

    There is a lid to the box and access from above would be through the floor, so not an issue.

    There are some unsheathed cables outside the box, I haven't yet been closer to pull them out, there is also a collection of PE in the Wago strip, I'm guessing he ran out of terminal space. I'm pretty sure one of these is clamped around the earth sleeve

    The quality of the installation is just naff, including chewed out hole and spray foam, but I recognise that people have different levels and abilities of this. I'm not sure why the cables had to move from the original hole but I'm bored of asking my builder about cosmetic issues now.

    My concern is the gaping hole, my understanding is that it is not appropriate for electrical installation and that the cable entries should be sealed to prevent the spread of fire.

  • Is the ceiling that has been cut a fire break between 2 independent zones ?  If so then a hole that size might compromise it.

    Or to check this, is it 2 layers of plasterboard or it is the pink stuff that is fire rated?

    Normally in a 'standard'  house with 2 floors and one set of stairs, upstairs and downstairs are one zone, But situations like granny flats or a third habitable floor can change this.

    It's not exactly first class neat work but it may not be a wiring regs or building regs fail.

    There are some builders sadly who seem to specialize in bumbling along near the shallow end  of the acceptable.

    Perhaps if you have not seen it already ask for the paperwork - there should be new installation (or perhaps just minor works if its a small extension)   certs and the some test results. That often results in a rash of activity, and it not being available  would be  a regs fail, albeit a very common one.

    Mike.

  • So, the box is mounted on some boxing that runs front to back on the house, just the other side of the wall to the right is a steel, the plasterboard installed here was pink, I'm not sure and doubt that the plasterboard here is pink, definitely not double

    it is a normal standard house, I'm not aware of fire zones.

    I think the works fits as minor works as it was all modification of existing circuits, should I expect a minor works certificate? I think they are planning to provide EICR only