Cable size between equipotential earth bonding bar and distribution board in a Group 1 medical location
The IET regulations require that the resistance of the conductors, including the resistance of the connections, between the terminals for the protective conductor of socket-outlets and of fixed equipment or any extraneous-conductive-parts and the equipotential bonding busbar (EBB) shall not exceed 0.2 Ω.
However the cable connection between the EBB and the Main Distribution board, is not defined, (identified in red in the image below) - either in terms of:
 1 - maximum resistance
2 - minimum cable size
3 - if the cable needs to connect to the distribution board that serves the room or should go back  to the Main distribution board.
4 - if there are number of EBB's can they be connected by a single cable in a daisy chain arrangement back to the distribution board.
Is any able to provide guidance on the four questions above?
  • so where, according to Section 419, disconnection times can't be met, and supplementary local equipotential bonding is applied, the touch-voltages are limited
    Although it us unusual for section 419 to apply - in common circumstances ADS for all the circuits in the location will work well within the times specified in section 411 (let alone 5s), but still supplementary bonding (in medical locations) is required. So I suspect it's as much a case of reducing touch voltages during ADS disconnection times as far as reasonably practical, rather than just covering cases where ADS doesn't occur (in time).
    Ditto in bathrooms - supplementary bonding is still demanded where not all circuits have 30mA RCD protection - even if all circuits have disconnections times <0.4s by MCB or fuse.
  • So I suspect it's as much a case of reducing touch voltages during ADS disconnection times as far as reasonably practical, rather than just covering cases where ADS doesn't occur (in time).
    In general, yes, for socket-outlets and most equipment fed from the TN or TT supply where disconnection times cannot be met ... the medical IT system, slightly different perhaps as it's not designed to disconnect on first fault, but for those circuits, Ia would be selected for the protective device(s) that are intended to operate on a second fault.
    Agreed, although that still permits up to 50 V AC touch-voltage, which, granted, has not been seen to be problematic in causing death, but certainly I think it's the current [excuse the pun] thinking that 50 V AC wouldn't necessarily protect someone who is submerged in a bath.
    Sorry ... edited 3 Feb 2026 ... NOT AGREED after further reflection ... see response.
  • Ditto in bathrooms - supplementary bonding is still demanded where not all circuits have 30mA RCD protection - even if all circuits have disconnections times <0.4s by MCB or fuse.
    Not agreed in full ... the disconnection time might be reduced, BUT the touch voltage is not necessarily limited to 50 V AC or 120 V DC by the bonding. The provision of the RCD can't limit the fault current, only affect the time that the person is subjected to the touch-voltage.
    For the circuits where say a B32 provides ADS, the bonding resistance requirement is:
    R ≤ (50 V)/( 160 A) Ω, or R ≤  0.31 Ω ... which could exceed Zs  for the circuit in question ... and is likely to be greater than R2. Certainly, it's not guaranteed to reduce the voltage to 50 V if operating "at the limit" of the formula in Reg 415.2.2.
    Yes, in practice, the bonding resistance in a small bathroom might well be far, far lower than the maximum 0.31 Ω permitted ... and the actual touch-voltage would generally be reduced ...
    BUT, clearly, "limiting the touch voltage to 50 V AC" is NOT the intention of additional protection by supplementary protective equipotential bonding according to Regulation Group 415.2 (otherwise the formulas provided would actually achieve that ... which they clearly are not intended to, as per the discussion above).
  • "limiting the touch voltage to 50 V AC" is NOT the intention of additional protection by supplementary protective equipotential bonding
    Absolutely - I hope I didn't give the impression that I believed it did. I do however believe it's there to reduce touch voltages in general - even if it doesn't provide any unconditional absolute limit (not unlike main bonding in that respect). 50V (or 25V) for 5s just one representative point on the curve of what it must achieve.
  •   Thank you. I just wanted to push back on this a little bit, for a very good reason.
    Throughout my career, I've heard it said many times that BS 7671 has a 'maximum touch voltage' of 50 V AC or 120 V DC ... it certainly has been a belief among some on the industry that this is the case. I've heard it more, to be honest, from designers and engineers working on larger programmes, than electricians.
    I would agree that in practice the effective touch-voltage can drop significantly, and may get down to 50 V AC or less. In fact, in industrial plant rooms and large infrastructure, where a common bonding network is in place, and each room has its own earth bar or bonding ring conductor, the expected touch-voltage from AC faults can be much lower than 50 V.
    However, I can conceive of examples, particularly where there's a TN-C-S supply, where if you take the resistances to their maximum (say 0.31 Ω where circuits in the location are supplied with breakers with maximum rating of B32) then the touch-voltage might be reduced from, say, 110 V AC to 90 V AC, which isn't really that much of a reduction.
  • Its an interesting point, as in reality as far as hurting people is concerned, what is needed is an over-voltage versus time curve.
    It may be that the 'normal' disconnection times cannot be met - which assume exposure to either half supply voltage or almost all of it depending on TNx vs TT earths and time accordingly, but in practice there is a sliding scale of increasing danger from some slightly increased disconnection time, to a situation where the fault voltage persists forever and is never disconnected.
    Personally I feel that 50V is rather high for the never disconnect and victim  good contact case, but it pops up in tests for RCDs and 1667 ohm Zs examples, but equally,  in many situations an ADS that should operate in 400ms operating in say 600ms may not be the end of the world if the voltage rise could be nobbled just a bit more or perhaps the contact impedance to the victim increased (thinking of that gravel around sub-stations).
    The problem is it is totally impractical to calculate every combination, and even if you could, what would you do with the results. " Danger only for people with unusually sweaty palms and damp footwear, safe for everyone else" is not the pithy and clear sort of text for a triangular warning notice !
    But in many cases the 50V has to be a bit aspirational as the exact fault current path may not be as expected, so which resistances should we measure, or there may be other factors that make the situation either better or worse, and usually of course, better late than never, something will operate and cut the power.
    You mean like this one?
    https://commons.wikimedia.org/wiki/File:IEC_TS_60479-1_electric_shock_graph.svg
    Standards committees use the IEC 60479 series for this type of data, and consideration of relevant approaches to protection against electric shock.
  • You mean like this one?
    Although that's based on body current rather than voltage - which hides one of the unknowns - i.e. body resistance. It might well be convenient to assume 1kΩ and so read mA for volts but I suspect that's not always a safe assumption.
  • Although that's based on body current rather than voltage - which hides one of the unknowns - i.e. body resistance. It might well be convenient to assume 1kΩ and so read mA for volts but I suspect that's not always a safe assumption.
    There is other data in the series of standards that helps with the different variations - this particular one is body current vs duration as you say.
    Voltage vs harm is very difficult, especially bathroom (if we are talking bathroom bonding), and certainly 50 V AC definitely not good for someone immersed in a bath indefinitely ... neither is the 90 V in my example, even disconnecting in 0.1 seconds !
    In dry conditions, it might be OK for most people wearing footwear. Bathroom, someone immersed, not so sure at all.
    In any case, BS 7671 is not intended to protect everyone all the time ... just most people most of the time. The 5 s disconnection time for distribution circuits in TN systems, and 1 s in TT systems, is a case in point.
  • someone immersed in a bath indefinitely
    Once you get past 5 s, the zones on the graph do not change.