Checking Iz
From BS7671
Method is used in items 5.1 and 5.2 Ib or In / Correction factors
But it is possible to get incorrect coordination with cable calculations that seem acceptable?
Sorry, this must be painful for you.
It is worth noting that not all books use the same notation for the letters, although these days mostly they do, and I find it helpful to have a 'plain language' description of what is happening.
or the protective device might trip during normal operation, and
which is the cable's rating.
Or the cable may be overloaded.
Of course once exams are passed you then will realise its not really always true - the limiting of the load current could just as well be at the load end or the origin - Perhaps consider a single 13A fused spur, on 2.5mm2 fed by a 20A or even 32A MCB will be fine, as the 13A fuse means the cable cannot be overloaded even though the circuit protection appears to be 32A.
More generally odd socket circuits are usually the ones where it is hard to be sure as you are often not really sure what might one day be plugged in and it maybe looks a if the breaker is too small, - perhaps a single 20A breaker feeding half a dozen BS4343 style 16A sockets for kit in a small workshop looks undersized, when the nature of the loads and the use pattern means it really isn't.
Then there is the matter that short duration overloads like motor startup in-rush may trip the breaker, but assuming they don't, the cable is fine with it, as it takes several minutes to warm a large bundle of cables and the grouping derating can be pushed quite a lot, if cables are not all fully loaded at once for a long time.
It is certainly worth keeping your wits about you above and beyond the algebra.
Mike
Sorry, this must be painful for you.
Not at all!
But I think I’ve got it.
It is basic transposition.
Sorry, this must be painful for you.
Not at all!
But I think I’ve got it.
It is basic transposition.