but a definition cannot contain the word, "or".
I think it's just a wordsmiths way of saying between 0.0 and 6.0mA
- Andy..
Then say so!
I think that you are correct (as ever) and the clue may be the "EN" in the document reference, but if you delete, "the value 0 or a", the meaning of the definition does not change.
Of course, if wordsmiths got it right first time, every time, there would be no amendments and no need of appellate courts (of which I have experience).
but
but for a half-wave pulsating current, it is half the peak value.
Is also not true I'm afraid, - its only about 33%, as half sine waves are bottom heavy, not a triangle... and yes we do have pantomimes.
But actually the whole thing could have been solved by actually showing, and annotating the waveform intended, by providing the existing oscillogram with labelled axes. Sadly that was not done.
Luckily perhaps we don't need to worry about it, as we only have to test RCDs at 250mA RMS with a sinusoidal AC. But it does rather beg the question of what happens with other waveforms, and if makers are in fact all testing in the same manner.
I don't have a problem with the word "or".
For 150 360ths of the cycle period it is at 6mA, for the rest, it is zero,
The problem is, that is not describing a DC, by any stretch of the imagination. It may be unipolar - i.e. non-reversing, but the one thing is is not is steady over time.....
They meant, and should simply have said, a square wave with an asymmetric duty cycle.
Oh yes it is.
Mike, you appear to be thinking of the average current, which is indeed about a third.
An alternating current reverses direction periodically. a direct current is one which does not. So long as the value is always zero or positive, it is d.c. It does not have to be smooth.
hmm..
Would you consider a unipolar square wave, or a triangle wave where the lower crest is at zero, as examples of DC?
I would not, because in addition to a DC term (0Hz, non changing, there for 'ever' or at least for the duration of the measurement) , there is a clear fundamental frequency, and some harmonics...
I agree there is a de-minimis case where the 0Hz term dominates - a DC with a bit of ripple on it is a common situation and makes sense described as such.
I might even consider the output of a 3 phase bridge to be in that class, but I'm not sure I'd consider something that fell to zero for a non-trivial part of the time to be quite the same.
I'm not sure how well that fits with the more 'power electrical' definitions, it is certainly open to more than one interpretation.
Perhaps we should re-introduce the term "continuous current"....
I think that I can see Mike's point. Whilst square-wave d.c. might be useful, e.g., for a flashing lamp, I suspect that the usual aim is to obtain smooth d.c.
Save that, for example, your 42 mA half-wave rectified d,c, superimposed upon 6 mA of smooth d.c. would be continuous.
Here is a Boxing Day question for all of you. It may be unlikely to occur, but if you had one device on a circuit with a fault to ground of 15 mA r.m.s. a.c. and another one with a fault of 15 mA r.m.s. half-wave rectified pulsating d.c., would a 30 mA type A RCD trip?