My war against dual rcd boards
As each (RCD) Residual Current Device must not have more than 30% leakage current on it.
It's hard to see how dual (RCD) Residual Current Device boards can be fitted at all these days.
i come across so many dual rcd boards with solar, evse and heat pumps on them, these have all been recently installed.
i wonder if BS7671 should state: Dual (RCD) Residual Current Device boards shall not be fitted, unless it can be shown (and documented) that they are suitable for the combined leakage currents expected .
otherwise developers will keep specifying them and i will have keep educating them on the many reasons a type A rcd should not be shared with other equipment!.
maybe manuafactuers instructions should also state : not suitable for a shared rcd, for certain equipment.
  • We need to take care with the peak, average (mean) and rms values of such signals.
    The 'pi' value keeps cropping up in a lot of situations (e.g. see also noise bandwidth vs signal bandwidth factors).
    As an aside, what is truly missing, is the explanation as to how/when these half sine [pulsed DC] style currents actually 'blind' the RCD. The pragmatic engineering/ material/physics are just (if not more) interesting than the mad/bad maths definitions Smiley.
  • ... re-introduce the term "continuous current"....
    maybe we should, but I think we'd have to agree what we meant by it first, which is kind of where we came in.  If we assign a single figure to something that is changing, are we refferring to  its mean, its RMS or its peak ?
    I'm not sure..
  • fault to ground of 15 mA r.m.s. a.c. and another one with a fault of 15 mA r.m.s. half-wave rectified pulsating d.c., would a 30 mA type A RCD trip?
    haha - maybe only  half the time ;-)
    you have defined exactly what you want, The sum of these upper 2 current traces, making the lower one
    We do not, however, as we have just discussed,  know for certain what the RCD spec actually means.
    PS for those interested, this is a simulation in LTspice, a tool I find helpful for this sort of stuff.
    This is the circuit being simulated.
  • haha - maybe only  half the time ;-)
    Mostly not, IMHO.
    If my maths are correct, the RMS value of the combined current is only 16.8 mA.
    But is, "mostly not" (or 50% of the time) a single RCD being exposed to an imbalance many times, or many RCDs being exposed only once?
    I think that we are all agreed on that. :-)
    P.S. this discussion beats the dross on the telly by a country mile.
  • I have added the RMS calculations to the simulation above (and updated the screenshot image in the post above, to reflect that just in case someone else wants to know how to try this sort of thing at home ) and the combined RMS is not as low as you might think, coming in at almost exactly  27mA. - it is not simple power addition (which would be root of sum of squares - think Pythagoras) because they are synchronous functions, - that is to say the peaks of the rectified and un-rectified waveforms are always aligned, and  not independent of each other and those peaks, while only there half the time, count for most of the RMS energy.
    The spice log is as follows.
    I appreciate that there are quantisation errors, so the nominal 15mA RMS in the 2 limbs is not quite, but this still illustrates the point
    It may help to visualise this by considering the power as a function of time, rather than smoothed over many cycles,
    regards
    PS schematic edited to create named nodes r1 and r2 so that we can plot the current in the component times the voltage across it with a meaningful name.
  • you appear to be thinking of the average current,
    very true, indeed I am, my mistake and while embarrassing it sort of reinforces the  point that it is important to be clear about these things, and easy to be confused ! Oops.
    PS missed this post at first as the website had carefully folded it away...
  • what is truly missing, is the explanation as to how/when these half sine [pulsed DC] style currents actually 'blind' the RCD.
    well in a few experiments I did here at home some years with an old 'AC' type RCD, they really don't seem to - so at least one manufacturer probably only needed to change the label, rather than the internals of their design. Equally a large smooth DC clearly does blind the RCD - as the D-lock series of meters clearly demonstrated, presumably by saturating the magnetic core, so it forgot to be a transformer at all, but there is an element of sneaking up on it, so at no time is the rate of change large enough to induce a significant secondary voltage.
    The problem is that it is no easy to be sure for some generic RCD, as the saturation behaviour will be horribly dependant on material choices and construction layout of the magnetic behaviour.
  • The other "problem" is that we generally don't have a good handle on the magnetics that cause the perceived 'average dc' to create the blinding effect.
    I've long thought it's probably a combination of the ferrite ring/core's saturation and hysteresis that shifts the operating point of the putative 'difference current transformer' to a point that has a low effective turns ratio (which would mean the trip solenoid would not activate at the expected [AC] leakage current).
    The saturation & hysteresis are determined by the specific material / ferrite in the particular RCD / GFCI brands. so likely to be highly variable as to test outcome for our general test of a random spare RCD from the disposal pile [I've recently pulled apart an old BG CUR8030 to try and see what is really in there]
    Average DC may not be the [pure] problem.
    Found https://physics.stackexchange.com/questions/60194/equation-describing-magnetic-hysteresis as a description of the equations for the magnetics. Yet to study it.
  • easy to be confused ! Oops
    derivation by integration is left to the student
    I too confused myself. When adding full-fat and semi-skimmed currents, I forgot to take into account that the relationship between RMS and peak values is different, and accordingly, the equations of the sine waves are different.
    I now have 15 + 15 ≈ 27.7, which agrees with Mike's value, subject to "quantisation errors".
    I have re-done my algebra and find:
    So where both components are 15 mA, the total is √(2 + √2) x 15 mA ≈ 27.7 mA
  • That is a reassuring result, and yes, pythagoras plus the cross term that makes all the difference looks right to me. I'll allow the 700micro-amps as the sort of thing that LT spice does not get right when it does its 'join the dots' integrations rather than  the pure maths. I will own up to being very good at losing factors of pi, 1/e and so on, when I do algebra under pressure and therefore I often use numerical tools like LTspice and others as a means to get close enough, when perhaps I should be reaching for a pen and thinking more.
    Now, if only it was as simple as the RCD tripping on any repetitive waveform with the correct RMS value, then a device designed to trip at some point below 30mA on a sine wave probably would on this too. However, as noted in the other post, the physics conspire to make it very hard to say much with any certainty at all beyond ' it'll need to be experimentally determined'. I think here transformer core saturation is more important than hysteresis, but that is probably one of the most material dependent parameters.
    I don't have a reliable set of saturation models for anything beyond the simplest representation of materials, and worse, while some pretty complex models exist, (Wolfarth, Stoner, 1940s, and Jiles- Atherton in the 1990s) I'm not sure that anyone really has one that is a good fit to reality for generic real materials over a wide range of conditions.
    LT spice does include a modified Chan model, as per this patent, https://patents.google.com/patent/US7502723 and certainly can be used to show saturation-like  trends that look more or less correct, but I'm not sure I'd want to design anything critical with it.