My war against dual rcd boards

As each (RCD) Residual Current Device must not have more than 30% leakage current on it.
It's hard to see how dual (RCD) Residual Current Device boards can be fitted at all these days.
i come across so many dual rcd boards with solar, evse and heat pumps on them, these have all been recently installed.
i wonder if BS7671 should state: Dual (RCD) Residual Current Device boards shall not be fitted, unless it can be shown (and documented) that they are suitable for the combined leakage currents expected .
otherwise developers will keep specifying them and i will have keep educating them on the many reasons a type A rcd should not be shared with other equipment!.
maybe manuafactuers instructions should also state : not suitable for a shared rcd, for certain equipment.
Parents
  • Three days ago I said:

    ”The question that Graham asked was quite specific:

    However, if the lamp is damaged, and the user is being protected against accidental contact with live parts, say after the rectifier, would the type AC RCD operate is perhaps another?”

    in that he said “after the rectifier”, so assume there are some diodes charging a capacitor, which discharges to supply the DC current, and the input current is 25 mA at 230 volts, what is the DC output current and voltage?”.

    So presumably after the rectifier the current and voltage is peak, not RMS? So if the current and voltage is 25 mA at 230 volts AC measured RMS, then after the rectifier it should be 35,35 mA at 325 volts pulsed DC unless there are a few more electronic components to drop the voltage?

  • If it's a single loop its the same current all the way around the loop.

    Quite so. If the (earth) fault is after the rectifier, the "pulsed d.c." flows through the RCD, which is where the problem lies. If the type AC RCD does not trip, lives could be at stake.

    And superposition

    OK, so you have a 30 mA RMS half-wave rectified (pulsed d.c.) current and superpose 6 mA of smooth d.c. What is the combined RMS current?

  • If the type AC RCD does not trip, lives could be at stake

    Which is the point.. (why we don't like RCDs that become 'blinded' by average DC flows)

    The simplistic assumptions (e.g. no inductive/capacitive energy storage/filtering) produce worst case figures. 

    The very sharp corners between half cycles aren't that realistic and, if Fourier analysed, imply a high frequency harmonics content, which tends to be filtered by the general wiring etc (without additional components).

    BigClive did some video on the workings of diode bulbs - worth looking at. I can't remember if the ones he looked at had a half or full wave rectification.

    There are problems of nomenclature in the attempted mixing of the two signals, in that often the first includes the second (commonly because of an arbitrary zero marking).

    A pulsed DC is a smooth DC and a pure AC (i.e. 'centred' about that smooth DC level)

  • A pulsed DC is a smooth DC and a pure AC (i.e. 'centred' about that smooth DC level)

    Oh no it isn't (do we still have pantomimes?).

    BS EN IEC 61557-6:2021 4.2.1 Note: A smooth direct current is a current with less than 10% AC ripple (peak to peak).

    So-called, pulsed d.c. could have no smooth component.

  • problems of nomenclature

    Exactly. Given that definition, the half wave rectified shape can never contain any DC component (which by most definitions is the 'smooth' component).

    Probably drop into the 'superposition' of components discussion here. "Clearly defined areas of Doubt & Uncertainty"

  • I agree that there is a problem with nomenclature.

    BS EN 61008-1:2012+A12:2017 hardly helps. Under, "definitions" at 3.1.3: pulsating direct current current of pulsating wave form which assumes, in each period of the rated power frequency, the value 0 or [my emphasis] a value not exceeding 0,006 A d.c. during one single interval of time, expressed in angular measure, of at least 150º

    Please forgive me if this seems pedantic, but a definition cannot contain the word, "or".

    BS EN 61008 specifies 3 groups of tests for type A RCDs: sinusoidal a.c.; pulsating d.c. (assuming a value of 0 for at least 150º of the cycle); pulsating d.c. superimposed by a smooth direct current of 0.006 A.

    So I think that we need to be careful what we mean when we say, "pulsed d.c."

    I'm not sure of the exact derivation, but the IET Wiring Matters article concurs:

    'When the Type A setting is selected on the instrument, a half wave pulsating residual test current superimposed on a smooth direct  current of 6 mA is produced, which effectively applies a 1.4 multiplier to the rated residual current (IΔn). For example, if the 30 mA setting is selected, the RCD will be subjected to a test current of 42 mA (30 x 1.4 = 42 mA)'

    That may well be an error.

    The manual for Megger 1700 series instruments states:

    'Type A' RCDs are sensitive to pulsed DC as well as AC fault currents, and are tested with a pulsed waveform. The RMS current is √2 x the rated operating current of the RCD.

    There is no mention of a smooth component.

  • but a definition cannot contain the word, "or".

    I think it's just a wordsmiths way of saying between 0.0 and 6.0mA

       - Andy..

  • Then say so!

    I think that you are correct (as ever) and the clue may be the "EN" in the document reference, but if you delete, "the value 0 or a", the meaning of the definition does not change.

    Of course, if wordsmiths got it right first time, every time, there would be no amendments and no need of appellate courts (of which I have experience).

  • but 

    but for a half-wave pulsating current, it is half the peak value.

    Is also not true I'm afraid, - its only about 33%, as half sine waves are bottom heavy, not a triangle...  and yes we do have pantomimes.

    But actually the whole thing could have been solved by actually showing, and annotating the waveform intended, by providing the existing oscillogram with labelled axes. Sadly that was not done.
    Luckily perhaps we don't need to worry about it, as we only have to test RCDs at 250mA RMS with a sinusoidal  AC. But it does rather beg the question of what happens with other waveforms, and if makers are in fact all testing in the same manner.

    Mike.

  • I don't have a problem with the word "or". 

    For 150 360ths of the cycle period it is at 6mA, for the rest, it is zero,

    The problem is, that is not describing a DC, by any stretch of the imagination. It may be unipolar - i.e. non-reversing, but the one thing is is not is steady over time.....

    They meant, and should simply have said, a square wave with an asymmetric  duty cycle.

    Mike.

  • but for a half-wave pulsating current, it is half the peak value.

    Is also not true I'm afraid, - its only about 33%, as half sine waves are bottom heavy, not a triangle...  and yes we do have pantomimes.

    Oh yes it is.

    Mike, you appear to be thinking of the average current, which is indeed about a third.

Reply
  • but for a half-wave pulsating current, it is half the peak value.

    Is also not true I'm afraid, - its only about 33%, as half sine waves are bottom heavy, not a triangle...  and yes we do have pantomimes.

    Oh yes it is.

    Mike, you appear to be thinking of the average current, which is indeed about a third.

Children
  • We need to take care with the peak, average (mean) and rms values of such signals.

    The 'pi' value keeps cropping up in a lot of situations (e.g. see also noise bandwidth vs signal bandwidth factors).

    As an aside, what is truly missing, is the explanation as to how/when these half sine [pulsed DC] style currents actually 'blind' the RCD. The pragmatic engineering/ material/physics are just (if not more) interesting than the mad/bad maths definitions Smiley.

  • you appear to be thinking of the average current,

    very true, indeed I am, my mistake and while embarrassing it sort of reinforces the  point that it is important to be clear about these things, and easy to be confused ! Oops.

    Mike.

    PS missed this post at first as the website had carefully folded it away...  

  • what is truly missing, is the explanation as to how/when these half sine [pulsed DC] style currents actually 'blind' the RCD.

    well in a few experiments I did here at home some years with an old 'AC' type RCD, they really don't seem to - so at least one manufacturer probably only needed to change the label, rather than the internals of their design. Equally a large smooth DC clearly does blind the RCD - as the D-lock series of meters clearly demonstrated, presumably by saturating the magnetic core, so it forgot to be a transformer at all, but there is an element of sneaking up on it, so at no time is the rate of change large enough to induce a significant secondary voltage.

    The problem is that it is no easy to be sure for some generic RCD, as the saturation behaviour will be horribly dependant on material choices and construction layout of the magnetic behaviour.

    Mike

  • The other "problem" is that we generally don't have a good handle on the magnetics that cause the perceived 'average dc' to create the blinding effect.

    I've long thought it's probably a combination of the ferrite ring/core's saturation and hysteresis that shifts the operating point of the putative 'difference current transformer' to a point that has a low effective turns ratio (which would mean the trip solenoid would not activate at the expected [AC] leakage current).

    The saturation & hysteresis are determined by the specific material / ferrite in the particular RCD / GFCI brands. so likely to be highly variable as to test outcome for our general test of a random spare RCD from the disposal pile [I've recently pulled apart an old BG CUR8030 to try and see what is really in there]

    Average DC may not be the [pure] problem.

    Found https://physics.stackexchange.com/questions/60194/equation-describing-magnetic-hysteresis as a description of the equations for the magnetics. Yet to study it.