Plug-in Solar supposedly going to be 'easier'?
Hi all, new to the forum.
I've been reading (various media outlets are running with the story) that the government is planning to make it easier (no mention of safety) for consumers to connect solar PV panel inverter directly to the mains using a 3 pin plug and socket arrangement.
Considering all of the current guidance regarding the connection of a solar PV inverter to the mains (dedicated circuit, own RCD, no 3 pin plug), how is this all of a sudden going to be 'safe'?
The argument that 'Balcony Solar' is all the rage on the continent surely doesn't negate the potential risks all of a sudden. Surely the IET is in discussions with government and arguing that the dangers cannot simply be swept under the carpet?
  • Indeed - the motors on most electric cars are in effect stepper motors, and the battery DC is gated onto each set windings in turn, cycling the effective polarity, to pull the magnet around one 'click' at a time at speeds of few Hz up to ~low kHz..
    Battery voltages seem to vary quite considerably between makers, - yes 350-400V is one standard, but so is 250-300 for small vehicles, and then 700-800V and even 800-900 for larger sportier cars. This is all about keeping the currents and wire sizes manageable.
    The actual Li-ion cells are between 3v (flat) and 4.1V (full charge) but are wired in complex series and parallel combinations to get the desired current capacity and voltage,
    To have an external  DC charger is not as convenient as it might seem, except when  the cell configuration for the specific vehicle is known, & even then the charger has to modulate its output voltage during the charge cycle to stay within a voltage-dependant safe current envelope as the cells charge.
    So using the on-vehicle charger that is carefully matched to the battery, and supplying it with a mains-like inverter-derived waveform, is generally still the most effective and certainly the lowest risk (and future proof for any new vehicle battery configuration).
  • UK regulations do not allow plug-in solar to be used in the UK
    Random thought - what happened to the CE/UKCA marking system? - presumably they shouldn't have been let onto any part of the EU market  unless they complied with the requirements of CE marking ... and presuming they did - wouldn't that (legally) make them acceptable for the UK market? (Yes, I did hear about so called Brexit, but I thought all the technical standards remain the same and the same principle holds, if by a national bit of legislation).
  • A CE mark means that the manufacturer declares it meets the required parts of the relevant product standards, generally for electrical kit, usually the low voltage directive, and one or more EMC standards, and for things that qualify, also the  machinery directive, no ensure it is not going to maim someone,  or going to burst into flames or leach dangerous chemicals...
    That may include the plug and socket regs, for things intended to plug into a 13A socket domestically, but does not include for example any extra requirements imposed by the BS7671, or the ECSQR.
    It may or may not mean the manufacturer has actually done any testing, the responsible ones do, but they may have just created the declaration.
    At the moment in terms of product standards, the VDE have one, but its not Europe wide.
    https://www.vde-verlag.de/normen/0100923/din-vde-v-0126-95-vde-v-0126-95-2025-12.html
    The maximum permissible feed-in power of the inverter was set at 800 VA, in line with the amendment to application rule
    E VDE-AR-N 4105:2024-10 "Generation systems on the low-voltage grid."
    The maximum permissible total module power has been set at 800 Wp + 20% (i.e., 960 Wp) if the plug-in solar device is equipped with a 'household plug' (that is a Schucko plug in Germany).
    The maximum permissible total module power rises to 2000 Wp if the plug-in solar device is equipped with a 'special energy plug', ' in accordance with DIN VDE V 0628-1 (VDE V 0628-1::2018-02)  This sort of thing is in use now for higher power systems.
    In the UK to meet BS7671 that would at least need a fused spur, maybe a fused RCD spur., or better a dedicated radial.. It's not shuttered so suffers the same problem of not meeting UK regs as the  IEC 60309 ('blue plug") caravan hookups, though really its a lot harder to touch anything nasty.
    Regards Mike
  • After some brief reading, I think that the Electrical Equipment (Safety) Regulations 2016 allow a CE marking to be accepted in lieu of UKCA. However, Reg. 3 excludes plugs and sockets:
    (2) These Regulations do not apply to—
    (e) plugs and socket outlets for domestic use;
    So, we seem to be back to the Plugs and Sockets etc. (Safety) Regulations 1994, which Graham mentioned yesterday.
    I see no reason why the German standard could not be adopted by UK law. However, if you have to get a sparks in to install the socket (assuming that you have a spare single gang socket, and that the terminals will accommodate 2 x 2.5 mm² of conductor) or even worse, a new circuit, it rather defeats the simplicity of plug-and-play.
  • Regulation 716.514.1 requires clear labelling at the consumer unit, meter position, and point of connection to identify that a prosumer installation is present and to indicate the presence of multiple sources of supply
    How could this ever be a requirement for an installation that had no "fixed wired" (for want of a better term) generation (even if it is 712 not 716 ... but MORE FUNDAMENTALLY 514.15.1, which is, to be brutally honest, absolutely necessary for conformity to the EAWR and CDM Regulations in ALL installation (that is, domestic, or otherwise, and regardless of whether the project is 'CDM notifiable') ?
    The installer would never be aware of the connection of the pluggable generation ?
  • I'd hope that fitting just one socket, either as DIY job, or getting someone in, would not be as disruptive as a full blown set of solar panels on the roof type installation, but cost  more like getting a new line put in for a new cooker position or something.
    And we followed the VDE approach,  it would only be needed for those above the 800W (which in Germany is 800 +/- 20%, so 960W max) so those customers with more cash to lay out.
    If we adopted this, it might we as well to let the plug and socket regs permit both these and  the caravan style blue sockets on domestic property as well.
    I'd also like to hope we did not need the installer to go on some special  course just to do that, and then try and recoup the cost from the customers (MCS like)
  • And we followed the VDE approach,  it would only be needed for those above the 800W (which in Germany is 800 +/- 20%, so 960W max) so those customers with more cash to lay out.
    That would still leave us with the prohibition of the use of BS 1363 plugs.
    However, there may be a loophole.
    How about leaving the Schuko plug on? Use a conversion plug to BS 1363-5:2023.
    1 Scope
    Conversion plugs specified in this part of BS 1363 are intended for the connection of loads to socket-outlets; they are not intended for [my emphasis] the connection of electrical power generators to socket-outlets.
    That is not exactly a prohibition, is it?
  • Meanwhile, over on Ebay.