Upstream downstream RCD test

GN3 advises that the test should be conducted upstream neutral to downstream line. It would appear that there is a functional reason but I would like some clarification. Yesterday I used the method to test several Contactum RCBOs. As per GN3 method at x1, all operated between 14 and 18ms. Reversing the probes to upstream line and downstream neutral, all operated but the instrument reported greater than 300ms. 

Parents
  • The basic theory of operation of an RCD tester is that it applies the test current and starts a timer.

    Its stops the timer and displays the result when the voltage on the line test probe disappears (due to the RCD contacts opening) or the limit of the timer is reached.

    If you have your line test probe on the ‘upstream’ line terminal of the RCD then it will remain live after the RCD contacts have opened.

    The RCD tester therefore will continue to see voltage on the line test probe, the timer will reach its limit and the instrument will display an over-range indication (for example > 300 ms). 

  • A useful point.

    I had expectations of some subtle internal influence within the RCD itself (like those DC current - type AC vs A discussions)

  • The RCD tester therefore will continue to see voltage

    not on a dual pole RCD ;) the opening of the neutral removes the supply to the tester as surely as opening the live would. However, the neutral break may be delayed after the live break, in 3 phase systems this avoids a load being strung between 2 phases, and in a single phase system it can still be used to allow a smaller contact and arc trap, as the main interruption occurs on contacts taking the live side. 300msec is rather long for that sort of delay however, and more like 10-20 ms is enough.

    Actually, ideally we'd measure for lost power between L and N on the load side of the RCD as that is what us being protected, and just introduce the fault between load side live and supply side neutral, as this is closest to emulating a live to earth fault.

    However a 2 pole tester is easier to understand and use,.
    Single pole breaking RCBOs need to be considered differently,. as here although the neutral side is sensed, it is never interrupted, so as suggested above, the device will trip, but the meter will time out. Mine stops after 2 seconds to spare setting fire to the fault path resistor.

    Are these single pole breaking RCBOs? 

    Mike.

  • Yes, single pole type A.

    Like Philip, I was expecting some explanation buried in electronics. Really good to know so thanks Ross and Mike. EDIALD!