Is the interconnecting cable between outdoor and indoor AC units classed as a control cable or power cable?

Is the interconnecting cable between outdoor and indoor AC units classed as a control cable or power cable?

Parents
  • Could be either ... or both.

    It's certainly part of 'machinery' as defined in the Supply of Machinery (Safety) Regulations, and therefore not completely in the scope of BS 7671 ...

  • wiring outside using SY or CY cable? 

    Plenty, and we use a lot of SY at work for voltages well above mains because of the RF shielding properties. Over a decade or so, if fully exposed to sun, and most is not, I'd expect SY failures at the clear jacket, and one can see the steel wires begin to rust where the outer has opened, and after perhaps another decade the shielding efficiency is lost. At that point it is pretty much as good as permanently installed  arctic flex.

    There is a lot of '7671compliant surface mounted and catenary slung twin and earth and arctic style PVC cable as well, that slowly embrittles, cracks and fails on a similar timescale. 

    As SY actually reveals it is failing, by the discoloration as the inner cores rust I personally like that inspectable quality. What I do not like is that almost no-one seems to have bothered to learn  what to do with the braid in termination. 

    I think it is a bit silly and unfortunate that there is no BS recognised standard for SY and CY cables, but they have their place (out of the sun, ideally).

    Mike.

  • recommend/demand a HO5 or 7 variant?

    Be careful with those cable specs - H only means it's a harmonized type, 05 or 07 the voltage range - so nothing there specifies UV resistance at all.

      - Andy.

  • recommend/demand a HO5 or 7 variant?

    EG    H07RN-F

    H07RN-F cable is UV resistant and suitable for long-term outdoor use, including direct sunlight exposure. Its robust PCP (polychloroprene) sheath protects against environmental, chemical, and mechanical stresses, making it ideal for industrial, agricultural, and construction applications

    Key features regarding durability include: 
     - Weather Resistance: Designed to withstand exposure to sunlight, moisture, and extreme temperatures (-30 - +60 degrees celcius).
     - Structural Integrity: The UV-resistant outer sheath prevents the material from drying out, cracking, or bursting when exposed to sunlight.Versatility: 
     - It is oil-resistant and flexible, commonly used for connecting machinery, heavy-duty tools, and temporary power supplies in open air

  • Exactly my question, this specified by the manfacturer, which distribute the same equipment around the world, ive never seen  this cable used in the UK for AC interconnections, but, this cable is not LSF so not suitable in some locations

    To another point on the design of the machine, it's also a requirement to design the installation and certify it, along with conplying with the UK regulations

  • Might be wroth speaking with Doncaster Cables Technical team?

    Tel 01302 821700

    email sales@doncastercables.com

    website.   https://doncastercables.com

  • To another point on the design of the machine, it's also a requirement to design the installation and certify it, along with conplying with the UK regulations

    With respect, you seem very reluctant to specify the standard or even law against which you are certifying compliance. Why is that please?

  • There are lots of regulations to comply with, BS7671, BS 5839, HTMs, and lets not forget the EAWR and CDM

  • Be careful with those cable specs - H only means it's a harmonized type, 05 or 07 the voltage range - so nothing there specifies UV resistance at all.

    That's why you have to use the relevant part of BS EN 50525 series ... it should achieve the same thing, but in the UK we'd certainly owant BS EN 52525 series.

  • Some makes of HO7 will be more or less UV resistant - its the letters that follow that matter.;-) 

    UV resistant Look out for third letter "N" without trailing qualifier numbers


    (See https://www.peakcables.co.uk/european-system-cenelec-codes/ for a fuller cable decoding of the system or even 

    https://myelectrical.com/notes/entryid/228/harmonised-cable-codes-and-colours 

    Then see https://myelectrical.com/notes/entryid/178/cable-insulation-properties for the chemical and physical properties of most common insulation materials.)

     Polychloroprene (brand name Neoprene synthetic rubber) on its own is rather better than say  PVC,  or indeed un-stabilised polypropylene or polyethylene, but even so  mil-spec versions exist that also have additional  UV stabilizers  put in to survive long term in the sun- 

    As a rule of thumb then unstabilised  PP or PE in full desert sun for about a year has lost 70% of flexibility and will show crazing and cracking right through if flexed

    PVC loses its chlorine from the surface and slowly crazes with the damage stopping after a few mm, unless the cracks are opened by flexing to allow the UV deeper.This is over a couple of years of full desert sun exposure.

    N on the other hand is dark so the UV does not penentrate and develops surface crazing due to loss of surface flexibility over about 5 times that period

    It is worth knowing what you are selecting. All cables last better out of sunlight but in the UK most days are not desert sun levels of UV , and even the 'wrong' cables can last many decades if at least partly shaded.

    Mike.

  • I believe it should be in scope of BS7671, as someone needs to certify it on install as compliant, and any cables used for Power should comply with BS or harmonised standards

    BS 7671 doesn't agree, see Regulation 110.2 (xi), noting that cables and wiring systems are electrical equipment (see definition of electrical equipment in Part 2).

    There is nothing to stop a designer, however, meeting the requirements of both BS EN 60204-1 and BS 7671, in cases where there are no conflicting requirements. And, to be clear, there are cases of conflict.

Reply
  • I believe it should be in scope of BS7671, as someone needs to certify it on install as compliant, and any cables used for Power should comply with BS or harmonised standards

    BS 7671 doesn't agree, see Regulation 110.2 (xi), noting that cables and wiring systems are electrical equipment (see definition of electrical equipment in Part 2).

    There is nothing to stop a designer, however, meeting the requirements of both BS EN 60204-1 and BS 7671, in cases where there are no conflicting requirements. And, to be clear, there are cases of conflict.