Looking to understand a ramp test result

I visited a customer today who had an RCD tripping after a water spill on a hot plate.

It was a single RCD protecting the entire installation, Hager type AC, been trying to persuade her to change the board for a few years.


The bit that I find strange is that the RCD was seeing 15.9mA of earth leakage, measured with clamp meter across tails. RCD also tripped in 133mS with 30mA test from a socket.

I then did a ramp test on both 180 and 0 degrees, from a socket with the installation powered, expecting a very low trip current due to existing high leakage, but it tripped at 21mA on both directions. Either I missed something or there is something I don't understand about the RCD testing setup? The one thing I can see with hindsight is that I didn't repeat the tests with the MCB's switched off.

So why would the ramp have gone so high before tripping? This is on a TT earth with Zs @ DB of 17.5 ohms. Currently installations insulation resistance is only 0.47 M Ohms ar 250V, line / neutral joined to earth. I hope this improves as the hob dries out.

  • It is not impossible, lets assume that most of the 15mA of standing leakage is capacitance L-E due to capacitors within mains filters in electronic loads plus  the natural capacitance of the wiring, which may also be on the high side, given it is a whole site figure.

    This current is at right angles to the applied voltage, or if you prefer, offset in time by a phase shift of 90 degrees.

    The insulation test tells us that less than 1mA is actually resistive leakage (0,25M ohms would do that.) so lets assume it is to all intents and purposes all capacitance.

    The ramp test however will be dropping in a binary weighted set of resistors or similar so the current it induces L-E will be in phase with the incoming voltage, and that stopped at just over 20mA.

    Adding the two, correctly, with a bit of pythagoras, we get Sqrt (20*20 +15*15 ) = sqrt (400+ 225)= sqrt (625) = 25mA at about 40 degrees to reality.

    For an elderly AC type, 25mA is in spec and not bad going.

    Then there is the odd mA of measurement rounding or meter uncertainty that I am not bothering with.

    hope this sets your mind at ease, there is almost certainly nothing bad going on,,

    Mike

  • Mike Thanks for the input. phase angle had crossed my mind. I was thought for cable inductance had more of an influence than capacitance, just means phase lag rather than lead.

    It will be interesting to see what happens over the next few days, there isn't much in the way of electronics, but it's a fairly big home, actually two on a single RCD, one unoccupied. At some point the owner is going to have to give in and change the CU, otherwise one day the rcd will trip and I won't be easily available across the road to help out.



  • Between  two rambling houses I suppose you may have half a km of cable in total and that could be 50nF ==  50,000pF, and at 50Hz that's about 60 kohms. On its own that accounts for perhaps 5mA  of leakage, but of course there could be  things like the capacitace from windings to core of a door bell transformer that might add a spare nanofarad. and there probably is some electronics. Circa 10nF of capacitance per device seems to be common. 

    If you want some numbers to conjure with, typical 2.5mm twin and earth measures between 60 and 100 picofarads from L or N to E with the unused core floating  and rather less L to N with E floating.

    Inductance per unit length is a measure of the energy stored in magnetic fields around moving charges (currents) and for that typical cable again is about 1 micro Henry per metre if only one core is carrying current; but if the flow and return currents in the cable are balanced so current in  L = minus current in N the round loop inductance is quite a lot less than the sum of the inductances of the two cores, as the magnetic fields oppose and overlap and partly  cancel - you may see as little as a few tens of nano-henries for a line pair.

    Capacitance is only a measure of the energy stored in the electric fields around and between conductors at differing voltages - there does not have to be anything that actually  looks like capacitor plates - that is just a good  shape for getting maximum C in minimum volume. (As a none standard capacitor shape, a plump human on a step ladder has about 500 - 1000 pF to the rest of the planet, and may feel a small tingle from a live wire despite being insulated to DC.)

    As per above, all these effects in wire alone can normally be safely ignored at 50Hz unless you have very long lengths or are interested in effects that are a small fraction of  the  currents and voltages in a typical load.


    Capacitance in parallel is more significant when the thing you are trying to measure is a low current, and the effect of a series inductance is more significant when it is carrying a large current. 

    Generally in the earth path the currents are small, so the fraction of the 230V across the capacitance will dominate.

    Mike.

  • Between  two rambling houses I suppose you may have half a km of cable in total

    That seems a lot. 10 circuits at 50 m each?

  • That seems a lot

    It is. it was meant to be a limiting upper-bound sort of figure, and assumes large houses, long submains to sheds down the garden etc.  I reckon a small bedsit flat may be a tenth of that...

    Mike.

  • One reel per circuit feels like a reasonable upper bound to me - considering we're talking total amount of cable rather than length to furthest point. If it's two houses,10 circuits across both might even be an under estimate,

       - Andy.

  • One reel per circuit feels like a reasonable upper bound to me

    The largest of the dwellings which are going up in a fancy development near here are around 160 m². Let's say roughly 8 m x 10 m for each of two floors. Downstairs is divided approximately diagonally. Modern open plan living limits sockets to outer walls. I reckon one socket circuit for each half plus the cooker. I have put the CU in the corner, but with rings the location is not critical. I get a total of about 70 m of cable for downstairs.

    Yes, I know that there will be an EVCP, which might be on the far side, and a heat pump round the back, but I still struggle to get more than 200 m even into what may be regarded as a spacious house nowadays.

  • Hello

    The answer may lie partly in the accuracy / tolerances of the measurements as they have been done with different instruments especially if you clamp meter is operating at the bottom of its range.  Some clamp meters are better than others and there will also be a tolerance on your RCD tester. Some clamp meters also pick up currents in adjacent wiring. As you say a test with all MCBs off so you are just looking at more defined test conditions would tell you more.