Hi All
I've attached a photo of a proposed EV charger position that will be fitted 2.5m from the LH metal fence (which is very long and surrounds the perimeter of the compound), however the parked car will most likely be parked within 2.5m in reality.
Details/concerns are:
3 phase PME supply
The metal fence reads 55 ohms to the MET
The EV charger will have PEN protection
Bonding the fence could pose a worse situation
currents could circulate in ground
PME services underground.
Would designating the car position at 2.5m from the fence with ground painting and signage be acceptable?
Is TT the only option even though underground services could be present.
Some people have said the PEN fault protection will be acceptable and not to bond.
If the IET gods could help it would be most appreciated.