DC isolators and RC62

The RISC document RC62 asks installers to carefully consider the need for DC isolators. It is not unreasonable for insurers to insist that the additional risk associated with the devices is appropriately assessed. This is one of two 100Kw inverters. They are both housed in a purpose-built concrete block structure abutting a large door manufacturing plant so fire spread may be reasonably controlled. However, do we really need to have an isolator on each string. Likely done this way as it connects to the individual MPPT inputs?

Parents
  • The COP is clear that the DC switch disconnector can be built into the inverter. Therefore, there is no regulatory imperative to have individual switch disconnectors for individual string connections. You can imagine the difficulty a contractor would have if he did not have a robust design strategy that considered and controlled the risk from the devices, if a damaging fire was traced to their use. 
    I acknowledge good reasons for their use and I accept that there is little substantive evidence to properly evaluate risk, but I would caution contractors and clients to avoid situations as indicated in the photo unless the insurer is consulted.

  • unless the insurer is consulted.

    One wonders about the expertise of the insurers in this. Is this a legal consult about contractual liability, or a knowledge consult about the insurance industry's hidden data?

  • You can imagine the difficulty a contractor would have if he did not have a robust design strategy that considered and controlled the risk from the devices, if a damaging fire was traced to their use. 

    On the other hand, if you were "gripping the bar" after someone died from electric shock while replacing a faulty inverter and council for the prosecution pointed to the (statutory) regulation 12 of the Electricity at Work Regulations and asked why you hadn't installed a suitable isolator... would you be comfortable relying on a mere code of practice (and not even a BSI one at that) for your defence?

    No easy answers I suspect.

       - Andy.

  • One wonders about the expertise of the insurers in this.

    I asked my insurers whether they impose any restrictions concerning solar PV, and the response was that they do not.

    So if I put a battery indoors and it has a melt-down, I shall still be covered.

    You can imagine the difficulty a contractor would have if he did not have a robust design strategy that considered and controlled the risk from the devices, if a damaging fire was traced to their use.

    Of course a wise contractor would have professional indemnity insurance, so in the event of a mishap, it would be a tussle between the contractor's insurer and the building insurer.

    I suspect that if an insurer were consulted, the best response that you would get is that the equipment must be installed to the applicable standards. I doubt that they will review the design, but perhaps they might in industry.

    regulation 12 of the Electricity at Work Regulations and asked why you hadn't installed a suitable isolator

    If there are "means of isolation" in the inverter, how do you isolate the panels in the event that the inverter has to be removed?

    I cannot see how installing a row of switches could lead to liability unless it could be shown that they were installed negligently.

    ETA: it makes a change to see good workmanship. :-)

  • A sensible engineering decision cannot be made without data - so does anyone know where all these fires from DC isolators were, and what was the cause?

    If it is the misuse of AC contacts on DC circuits, or breaking under-load using devices designed only to isolate when off-load, or overload due to inadequate current ratings, then  there is a need for better educational material and/or tighter product standards. The man on the ground acting as designer-installer is not well placed to make the decision in a vacuum.

    Advice to take reasonable steps to avoid without context is unhelpful. 
    There is a general problem, that except at night or when covered, solar panels cannot be turned off, and unplugging things while still energised is not without risk, especially in large systems using higher voltage strings near the kV level.

    The inability to isolate must be balanced against the risk of the isolator causing an extra problem.
    Mike.

  • Also need to separate the voltage level 'shock' risk from the current level 'arc'/fire risk. 

    Some things are good at managing the voltage disconnect risk, but unsuitable for the current disconnect risk, and vice versa.

    Meanwhile we should take care to identify which item is considered faulty at the point of disconnect (does it contain, or exclude the disconnection device itself?). [includes the 'quality' issue misrepresented devices]

    It's quite a multi-factorial problem.

Reply
  • Also need to separate the voltage level 'shock' risk from the current level 'arc'/fire risk. 

    Some things are good at managing the voltage disconnect risk, but unsuitable for the current disconnect risk, and vice versa.

    Meanwhile we should take care to identify which item is considered faulty at the point of disconnect (does it contain, or exclude the disconnection device itself?). [includes the 'quality' issue misrepresented devices]

    It's quite a multi-factorial problem.

Children
No Data