Neutral in the High resistance earthed systems

For High resistance earthed, LV systems, Can the neutral be used like this? Will there be any safety issues like increase voltage in the neutral?

Parents Reply
  • For systems that are fully IT, and you wish to control touch voltages, there is in effect a current limit - 10mA or less in the case of medical for example.

    In a the more general case of a  resistively earthed neutral but neither TN nor IT, this does not apply, and you need to look at both the ADS corner cases.

    M.